Wayne, 

 

That's because the GVFX3524 goes not provide any support for ground
switching.   If you install a Ground switching relay and isolate the
input neutral from the output neutral bus's this will get rid of this
problem... 

 

On a side note how did you get a utility (or have you) to approve a GT
inverter on a mobile trailer? 

 

Steve Higgins. 

Sr Application Engineering Mgr

Sub-Saharan Africa Business Dev Mgr. 

Outback Power Systems. 

19009 62nd Ave Ne 

Arlington Wa 98223

360-618-4313

 

 

From: [email protected]
[mailto:[email protected]] On Behalf Of Wayne
Irwin
Sent: Tuesday, June 01, 2010 9:30 AM
To: Wrenches
Subject: [RE-wrenches] Portable Solar Trailer w/ intermittent Ground
Fault

 

Hello Wrenches,

We have a 2KW portable unit with one Outback GVFX3524. Intermittently,
we have a problem feeding GFI breakers. 
Its the strangest thing, sometimes it trips GFI's and other times it
doesn't. Aside from the possibility that some of the GFI's aren't wired
properly we haven't been able to figure it out. We have it plugged into
a GFI at the shop (which is wired properly) and there is no problem.

I thought there was a previous string on this issue but could not find
it in the archives.
What do you recommend for grounding portable units and what
recommendations do you have from personal experience?

Thanks!

Wayne Irwin
Director of Engineering
Pure Energy Solar International Inc. 
State Licensed Solar Contractor
License # CVC56695 
[email protected] <mailto:[email protected]>  
http://pureenergysolar.com <http://pureenergysolar.net/>  
352 377-6527 Office
352 336-3299 Fax 

The content of this message is Pure Energy Solar Confidential. If you
are not the intended recipient and have received this message in error,
any use or distribution is prohibited. Please notify me immediately by
reply e-mail and delete this message from your computer system. Thank
you.



________________________________

Hotmail is redefining busy with tools for the New Busy. Get more from
your inbox. See how.
<http://www.windowslive.com/campaign/thenewbusy?ocid=PID28326::T:WLMTAGL
:ON:WL:en-US:WM_HMP:042010_2> 


MESSAGE CONFIDENTIALITY NOTICE:
This message (including attachments) is covered by the Electronic Communication 
Privacy Act, 18 U.S.C. sections 2510-2521, is confidential, and may also be 
protected by attorney-client or other privilege. If you believe that it has 
been sent to you in error, please do not read it. If you are not the intended 
recipient,you are hereby notified that any retention, dissemination, 
distribution, or copying of this communication is strictly prohibited.  Please 
reply to the sender that you have received the message in error, then delete 
it. Thank you.

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to