Hi fellow wrenches forgive me if this has been said. 
The AC is a special problem on MIcro inverters because the long runs modules to 
service are now in the AC section of the system.  The DC connections are very 
short.  The utility has a +- 5% normal tolerance, which leaves us with only 5% 
to count on.  If the grid is high any voltage rise would put us very close to 
high voltage shut down.  The manufacture is trying to help us prevent nuisance 
shut downs, and is looking for 1% voltage rise.  Voltage rise or drop is easily 
calculated in English units by Vr=2KIL/CM where K is the coefficient of 
resistance for copper (12.9)  I is the current in amps, (0.82x#of M190 
inverters) L is the one way length of the wire run.  or equally straight 
forward is Vr= 2LIR/1000 where the L is the one way length, I is the current as 
above, R is the resistance per 1000 feet of wire.  The CM and R values are from 
Chapter 9 Table 8 of the NEC 
Darryl

--- On Fri, 6/11/10, Jeff Yago <[email protected]> wrote:

From: Jeff Yago <[email protected]>
Subject: Re: [RE-wrenches] AC wiring loss on micro-inverters
To: [email protected], "RE-wrenches" <[email protected]>
Date: Friday, June 11, 2010, 5:42 PM

I just attended a training class in Philly last week by Enphase technical staff 
and my notes say they suggest up to 15 micro-inverters @ 190 watts each per 
string with no problem.  They also are now shipping their dual module 
micro-inverter which should help with this wire issue since this model #D380 
has two #M190 units built into the same box which is only slightly larger 
than a single micro-inverter.
 
Since this new dual micro-inverter does NOT have the AC pass-through wire 
built-in, you are no longer limited to the wire size that comes in and out for 
the 240 VAC connections.  HOWEVER, they require you to purchase this awful 
looking multi-tap pigtail cable for the AC connections which has a pre-wired 
connector spaced the expected distance apart the micro-inverters would be 
installed, and this is a $950 item for every six dual micro-inverters.  When I 
saw this thing I thought is was a python that had swalled six pepsi cans!  Not 
sure what this will look like on a roof or how well it can be hidden behind the 
array, but it uses a larger wire size so perhaps the wire loss issue has been 
resolved.
 
Jeff Yago
DTI Solar
 
Netscape.  Just the Net You Need.

-----Inline Attachment Follows-----

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




      
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to