I will set the transfer delay to zero next site visit. I did just confirm that the AC transfer control is set to GEN.

On Jun 15, 2010, at 9:01 AM, Steve Higgins wrote:

Transfer delay of 30 is too long with sensitive electronics. This means that when the AC input drops to 110VAC the inverter waits 30 cycles before we disconnect from the genset.



If the Ac transfer control is set to Grid instead of GEN then you would have to program these settings into the ADV/FX/GRID set points. When I visit sites I will usually program both GEN and GRID equal.



Steve Higgins.

Sr Application Engineering Mgr

Sub-Saharan Africa Business Dev Mgr.

Outback Power Systems.

19009 62nd Ave Ne

Arlington Wa 98223

360-618-4313





From: [email protected] [mailto:re-wrenches- [email protected]] On Behalf Of Jeff Wongstrom
Sent: Tuesday, June 15, 2010 6:37 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Gen set problems



Hello Steve,



In my case, I tightened the voltage window to 110 lower, 125 upper and the transfer delay to 30. This made no difference. I did not confirm SETUP/FX/INPUT ...ac transfer control set to GEN.





On Jun 15, 2010, at 7:15 AM, Steve Higgins wrote:




William,





Check to make sure what Input you have selected… go to SETUP/FX/ INPUT… Verify that you have the Ac Transfer control set to Gen.



Make sure that you have adjusted the transfer delay cycles in the right screen... ADV/FX/GEN under Transfer delay cycles… I would set this to 0.



As Mick said.. Check the Lower limit on the AC Voltage… ADV/FX/ GEN… AC2 Gen Lower Limit I would adjust this up to 110-112?



What does he have the cool down timer set to?



I would suggest 5-10 minutes Look under… ADV/MATE/AGS/SETUP… I would set this to at least 5-10 minutes just to let the genset cool off before shutting off.



Steve Higgins.

Sr Application Engineering Mgr

Sub-Saharan Africa Business Dev Mgr.

Outback Power Systems.

19009 62nd Ave Ne

Arlington Wa 98223

360-618-4313





From: [email protected] [mailto:re-wrenches- [email protected]] On Behalf Of William Miller
Sent: Monday, June 14, 2010 10:32 PM
To: RE-wrenches
Subject: [RE-wrenches] Gen set problems



Wrenches:

I have a customer that has a problem with a new generator. He has two VFX3648 inverters in Outback stacking. He acquired a new generator, a Kohler 12RES, a reputable make and model. Below is a description of the problem:

The 12RES seems to be operating OK except for one problem. At the end of a charging cycle, when the gen automatically shuts down and load goes back to the inverters, all lights, TVs, etc., flash, one TV shuts off, and a GFI trips. This has happened every time. It did not happen with the 15RES or the smaller back-up gen (which was disconnected manually). With the 15RES the same GFI would occasionally trip while the unit was charging and handling house load, but never at the auto shutdown point. I replaced the GFI, but it still trips. There are three GFIs in the house, but only one--always the same--trips.


I suggested he adjust the AC2/Gen transfer delay to a lower number. He reduced it to minimum and this did not resolve the problem. I also had him verify that the AC source is selected as generator, which it is.

Do you have any suggestions?

Thanks in advance,

William Miller





Please note new e-mail address and domain:

William Miller
Miller Solar
Voice :805-438-5600
email: [email protected]
http://millersolar.com
License No. C-10-773985

MESSAGE CONFIDENTIALITY NOTICE:
This message (including attachments) is covered by the Electronic Communication Privacy Act, 18 U.S.C. sections 2510-2521, is confidential, and may also be protected by attorney-client or other privilege. If you believe that it has been sent to you in error, please do not read it. If you are not the intended recipient,you are hereby notified that any retention, dissemination, distribution, or copying of this communication is strictly prohibited. Please reply to the sender that you have received the message in error, then delete it. Thank you.

_______________________________________________

List sponsored by Home Power magazine



List Address: [email protected]



Options & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org



List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re- wrenches.org



List rules & etiquette:

www.re-wrenches.org/etiquette.htm



Check out participant bios:

www.members.re-wrenches.org





MESSAGE CONFIDENTIALITY NOTICE:
This message (including attachments) is covered by the Electronic Communication Privacy Act, 18 U.S.C. sections 2510-2521, is confidential, and may also be protected by attorney-client or other privilege. If you believe that it has been sent to you in error, please do not read it. If you are not the intended recipient,you are hereby notified that any retention, dissemination, distribution, or copying of this communication is strictly prohibited. Please reply to the sender that you have received the message in error, then delete it. Thank you.

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re- wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to