Keith:

I believe it is rare that a PE stamp is required. A well laid out calc. sheet should allow a moderately trained plan checker to follow along.

I am in favor of strict standards. It seem there is a school of thought that says this is not feasible. I hope not. here's an analogy: As framing gets more complicated, is it OK for plan checkers and inspectors to throw in the towel and just allow the framers to figure it out? Or should consumers insist that proper standards be developed and enforced for their protection?

William Miller


At 10:07 PM 6/15/2010, you wrote:
William

Good points. One thing I'd like to mention out here in the 50th state- on the residential side, they don't do any calcs. They count on the installer. The electrical inspectors aren't privy either or aren't very interested. Even on some of the commercial projects, small commercial, they are taking the word of the PE that stamps the drawings. Just like electricians, some PE's are diving in to this and asking PV guys how to do the calcs, as they are more trained in the commercial strip mall, high rise, hospitality genre and not boned up on string sizing.