I just had my proposal for a supply side tap (between meter and main) of on a
residential system rejected by the inspector (CA) because he wants a letter
from the service panel manu detailing the proper method of making this tap and
that I must strictly follow it. This is a 1st for me, I've done lot's of
commercial supply side taps as well as residential in numerous jurisdictions
and this has never been requested. To make matters worse, the manu of this
service is Zinsco, no letters are coming from this long ago defunct company. IF
you could even get any manu to do this how many months do you think it would
take to get and after how many prods?
The inspector acknowledges that the NEC allows for supply side taps w/PV
systems as well as noting that nowhere in the NEC does it require this
permission letter. He says he found discussion about it on the 'net and that
some feel the taps violate the U.L. on the panel. I can see this take, but feel
a simple tap is not a significant "modification" to a listed panel and the
impacts on our installs is significant as those letters will not come easy.
Any thoughts?
Thanks,
-jeff o
>From the Solar, Wind and Hydro powered office of Jeff Oldham/Regenerative
>SOLutions
____________________________________________________________
Ditech® Official Site
Fast & Friendly Service. Apply Online and Start Saving Today!
http://thirdpartyoffers.juno.com/TGL3131/4c1a49d1bb4493d9946st06vuc
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org