My system always drops the slave inverter, mounted at the bottom, when the charge backs off. It is a FW 500 setup.

At 10:09 PM 6/21/2010, you wrote:
The inverters are mounted in a vertical orientation.

Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City,  CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/>www.berkeleysolar.com



----------
From: [email protected] [mailto:[email protected]] On Behalf Of jay peltz
Sent: Monday, June 21, 2010 5:31 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Outback Charging Method

Hi Mark,

In stacked systems I've usually seen the inverters not charging the same amount. Seems like they should share the charge as well as load, but doesn't seem to be the case.

Was the unloaded one above the other?

jay

peltz power
On Jun 21, 2010, at 2:39 PM, Mark Frye wrote:

Thanks Jay,

This came up because I was looking at the summary on the Mate during charging and it showed that one of the stacked slaves had 0.0kw charge power. Strangely enough, the ac charge current showed 16 AAC. This is how I got on the subject with tech support. They said that the 0.0 kw charge power was perfectly normal because the charge controller was trying to reduce the charge current by drop operation of one of the stacked inverters.

I always figured that the slaved stack would rise and fall in unison to meet the current demand.

I do have them running at variuos "power save" levels so I suppose it is possible that entire chargers are being dropped, but I thought that was only for managing the on/search mode on larger stacks.

I am guessing that this is more a matter of reporting errors in the mate.

Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City,  CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/>www.berkeleysolar.com



----------

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
NABCEP TM  Certified PV Installer
Office - 740-448-7328
Mobile - 740-856-9648  
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to