Jeff,

I've installed a few SQ Flex. There is no need to use Grunfos panels. I 
generally shoot for a reasonably hi voltage, say 130 to 170 vdc when going 
array direct (at least for more rigorous pumping requirements). The pumps will 
work (and seems do do good ) at even lower voltage , 60 is a low as I go.

For larger systems, in my case a 3hp 3phase, I am getting great results going 
hi voltage (say 400) array direct into an Aerovironment 3 phase inverter. The 
freq is wild, 30-60 hz depending on irradiance. This is primarily limited to 
standalone pumping sites where you do not already have significant inverter 
power.  The Aerovironment comes in three sizes and they are in the AEE catalog. 
They are pricey but for high power loads they might be a solution. In my case , 
I use about 3200 w (stc) of array to drive a 3 hp pump.

Don Loweburg