The propane and gasoline generators both ar premixed combustion and have a low 
efficiency at part throttle/ part load.  The Diesel does the best job of 
maintaining efficency at low load.   The outback can control its charging 
current to the load limit of the generator.  If the AC loads need more power 
the Outback can reduce the charging rate until the AC load diminishes.  

It takes a lot of words to describe and decide what is the correct generator 
sizing.
Darryl

--- On Wed, 7/21/10, Mark Frye <[email protected]> wrote:

> From: Mark Frye <[email protected]>
> Subject: Re: [RE-wrenches] Propane Generator, Dual Outback Inverters
> To: "'RE-wrenches'" <[email protected]>
> Date: Wednesday, July 21, 2010, 1:33 PM
> Can you say something more about the
> system?  Is there a PV component?  What
> is the size and type of the battery bank?
> 
> The thing I am beginning to understand about propane
> generators is that
> there is a problem with Outback charging re: partial load
> efficiency.  If
> the generator/chargers are sized to give a good C/10 bulk
> charge rate, then
> they will be running well below 50% load when they are
> providing a desirable
> absorption phase current. That's extended absorption run
> times at poor
> generator efficiencies. This also plays into having a
> generator that is
> sized for full AC loads and full charger currents. If you
> design for this
> case, but do not have large AC loads during charging, you
> will be well down
> into the 25% load on the gererator, very inefficient with
> propane.
> 
> I have had very good success with my Kohler 30kw REGZ
> 2-wire start propane
> generator in a lower elevation, California foothills
> location.
> 
> What exactly do you mean by harsh environment?
> 
> Mark Frye
> Berkeley Solar Electric Systems
> 303 Redbud Way
> Nevada City,  CA 95959
> (530) 401-8024
> www.berkeleysolar.com 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]]
> On Behalf Of Jason
> Szumlanski
> Sent: Wednesday, July 21, 2010 11:21 AM
> To: [email protected]
> Subject: [RE-wrenches] Propane Generator, Dual Outback
> Inverters
> 
> I'm looking for experiences/recommendations for a 15-20kW
> propane generator.
> It would be going in an off-grid system with dual Outback
> 3600W
> inverter/chargers. The excess capacity would power larger
> loads than the
> inverters can handle. Fuel economy and harsh environment
> performance are the
> top priorities (along with the ever important $).
> 
> Jason Szumlanski
> Fafco Solar
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
> 


      
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to