Darryl:

There is a scenario in which problems occur: If your loads exceed the generator capacity, the Outback system will fail. The Xantrex inverters are superior in this scenario in that they will transition to invert mode to synchronize with the generator and support the generator as long as the batteries will sustain the operation of the inverter.

William Miller


At 12:21 PM 7/21/2010, you wrote:
The propane and gasoline generators both ar premixed combustion and have a low efficiency at part throttle/ part load. The Diesel does the best job of maintaining efficency at low load. The outback can control its charging current to the load limit of the generator. If the AC loads need more power the Outback can reduce the charging rate until the AC load diminishes.

It takes a lot of words to describe and decide what is the correct generator sizing.
Darryl
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to