Just a minor point: the dash-two appendage brings a wet-rated wire from 75
deg C to 90 deg C. 

If you are not in a locale that argues for wet-rated wire and your specific
application does not argue for wet-rated wire, IMHO it is perfectly
acceptable to use THHN wire (90 deg C rated for damp environments) for
outdoors, attics and other extreme temperature conditions. Of course you
have to use good 3R boxes and rain-tight EMT connectors.

For us, it is easier to purchase and inventory just one wire type for
conduit runs, and we usually get the same price for THWN-2 as we do for
THHN, or close enough. In fact we almost never use #12 either for the same
reason.
 
Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
CA Lic. 854779, NABCEP Cert. 031806-26
[email protected]  
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885

 
________________________________________
From: [email protected]
[mailto:[email protected]] On Behalf Of Allan
Sindelar
Sent: Friday, July 23, 2010 10:04 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] #10 THWN-2

Mick,
-2 means 90 degrees C rather than 75. THWN-2 thus means that it is wet-rated
at 90C.  That is generally considered Code for arrays, such as if it is run
in NM flex conduit to a traditional module j-box. The j-box area may be
considered to be able to get hot enough to require 90C rated wire. Nowadays
with MC-type module leads, combiner boxes aren't subject to the same high
temperatures on the THWN as when they terminate in module j-boxes, and the
higher temperature rating isn't generally necessary.

Much of what I'm saying here is older John Wiles stuff.
Allan
 
Allan Sindelar
[email protected]
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com

On 7/23/2010 10:52 AM, Mick Abraham wrote: 
I'm sorry to broadcast my ignorance, but:

Could someone explain to me the significance of the -2 marking? Reply
off-list if you wish to save bandwidth...but other List members may also be
wondering... 

Thanks, 

Mick Abraham, Proprietor
www.abrahamsolar.com

Voice: 970-731-4675

On Fri, Jul 23, 2010 at 10:48 AM, Nick Soleil <[email protected]>
wrote:
I have specified THWN-2 for years, but occasionally will not be able to
source it!

Sent from my iPhone

On Jul 23, 2010, at 11:37 AM, "Peter Parrish"
<[email protected]> wrote:
We went through a similar problem with some beach communities here in SoCal.
Because of the high humidity (all winter and summer mornings) they wanted
THWN-2 for all conduit runs (as well as PVC instead of EMT). At first we
were charged a premium for THWN-2 compared to THHN. But then we found a
source at All Phase Electrical Supply Burbank CA (a part of CED) for THWN-2
#10 stranded @ $162.40/k-ft. Brand is En(m?)core Wire. THWN-2 listing is
printed on the insulation.
 
- Peter
 
Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
CA Lic. 854779, NABCEP Cert. 031806-26
[email protected]  
Ph 323-258-8883, Mobile 323-839-6108, Fax
323-258-8885                                                              
                                    
 
 
_______________________________________________ 

List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to