I'm with Dick on this one... Sure, I've seen a few good oopsies involving aluminum, (where the J box does the Salvador Dali thing)... but they're usually installed by "Uncle Larry" types... as long as the install is code compliant (Listed and properly installed), I don't think it maters much. db
Dan Brown
Foxfire Energy Corp.
Renewable Energy Systems
(802)-483-2564
www.Foxfire-Energy.com
NABCEP #092907-44
-------- Original Message --------
Subject: Re: [RE-wrenches] AL wire with DC
From: [email protected] (Richard L Ratico)
Date: Fri, July 23, 2010 6:18 pm
To: [email protected]
Dana,
Thanks for the input. Excuse me please, "OG jobs" are?
If the wire had been copper and didn't melt, but instead continued to arc,
would the resultant heat have eventually started a fire?
What type of splice was it?
Does no one else use Al for DC? Here in rocky Vermont/NH,
we use the same type aluminum URD cable for both AC and DC runs, but,
always installed in PVC conduit, never direct buried. Haven't seen
seen a problem yet.
Dick Ratico
Solarwind Electric
--- You wrote:
The problem with Al is that, IF there is ever a loose
connection, & associated arcing, that it melts not like
copper in the same situation which may arc but not melt.
I have come in on OG jobs where Al was employed and found J
boxes that were [sometimes wet] and had loose connections
and the splice was charred/melted and the AL wire was not
conducting & melted beyond use, directly at the splice. The
rubber linemen's tape was charred and there was a direct
short to the metal box which was at least grounded
correctly. I tend not to use Al based on this experience.
Thanks, Dana Orzel
Great Solar Works, Inc
E - [email protected]
V - 970.626.5253
F - 970.626.4140
C - 970.209.4076
web - www.solarwork.com
"Responsible Technologies for Responsible People since 1988"
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf
Of R Ray Walters
Sent: Friday, July 23, 2010 7:46 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] calculating DC voltage drop
I try to keep it in copper for DC, as I had always heard of
trouble with Aluminum on DC. (True or Old Wrenches Tale?)
We definitely go to Al on long AC runs, as its whats
available, and the cost difference becomes remarkable.
I've seen small cuts in Al, later corrode completely through
the conductor.(AC run) I'm not sure what would happen it
were DC.
Probably depend on whether it was positive or negative, and
which was bonded to ground? (either accelerate the
corrosion, or act as cathodic protection?)
R. Walters
[email protected]
Solar Engineer
--- end of quote ---
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________ List sponsored by Home Power magazine
List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org

