I think you may have some thing there.  It a bit out of the box however,   At 
C/10 one Magnum can handle 1000 AH battery.  But the magnums can not grid tie, 
so the GT would be left to the Outbacks.  Your idea is intregueing however.  I 
think there is a out of box solution for this problem.  
darryl

--- On Sun, 8/8/10, bob <[email protected]> wrote:


From: bob <[email protected]>
Subject: Re: [RE-wrenches] Advice needed on upsizing a battery & grid 
interactive inverter stack
To: "'RE-wrenches'" <[email protected]>
Date: Sunday, August 8, 2010, 9:39 AM








Can the Outbacks be mixed as ½ or whatever number be GT units and the rest be 
off grid so they can charge off a generator or better than that make the 
battery charging inverters Magnums, they give more charge for the bucks. They 
can feed a load panel on their own and charge the batteries off the generator 
when need be. I see no reason they could not be all hooked to the same battery 
bank but it better be huge (needless to say)!
Zantrex used to make a unit called “incharge” that I have used several times. 
It hooks to an alternator and gives you 3 stage charging. They worked quite 
well but I HATED setting them up. They have a set of magnetic switches in the 
potting that you had to activate to adjust, in sequence or go back to the start 
and do it again.
I absolutely hated the god forsaken things every time that I had to get near 
them, but if you can deal with the adjustments they worked well. Needless to 
say I would have liked knobs much better!
 
Later,
Bob Ellison
 

From: [email protected] 
[mailto:[email protected]] On Behalf Of Mick Abraham
Sent: Saturday, August 07, 2010 7:14 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Advice needed on upsizing a battery & grid 
interactive inverter stack
 
Thanks for the input, Daryl~ For now the prospect is considering sufficient 
power for a big energy hog home plus outbuildings. They'll probably get over 
that soon once the sticker shock sinks in. You asked, "how big a battery bank 
and how big a generator?" Mick replies: the whole hog system would 
need...guessing...about 500 kilowatt-hours of storage (~14,000 amp hours at 48 
volts), 70kW worth of inverter/charger, plus a lot of PV. A 48 volt generator 
seems not best because that would involve over 1,000 amps coming off the 
machine. Maybe multiple DC generators would be worth consideration. I see why 
you are pointing in that direction, Daryl, because if not for the generator 
problem the Outback GT system can go large.

 

Finding a 48 volt generator line with proper end of charge regulation is 
another challenge. Can any List member provide feedback on the Canadian mfr, 
Mechron?

 

Much appreciated, 



Mick Abraham, Proprietor
www.abrahamsolar.com

Voice: 970-731-4675



On Sat, Aug 7, 2010 at 11:19 AM, Darryl Thayer <[email protected]> wrote:




I have a functioning Outback system of 12 inverters, the original design was 
for 15 inverters. My system can sell up to 40 kW to the grid and I have seen 
pictures of systems up to 25 inverters.  How big a battery bank and how big a 
generator?  Realistically you may not want to charge over C/10    Have you 
considered a 48 volt generator?  

Daryl 

--- On Fri, 8/6/10, Mick Abraham <[email protected]> wrote:

From: Mick Abraham <[email protected]>
Subject: [RE-wrenches] Advice needed on upsizing a battery & grid interactive 
inverter stack
To: "RE-wrenches" <[email protected]>
Date: Friday, August 6, 2010, 6:17 PM


 

Yo, Mechanics~

 

A client is considering a "biggest ever for me" battery based power system. 
They will probably scale down their ambitions once the cost realities settle in 
but for now they've asked me to look for battery based inverter systems which 
can scale bigger than a triple stack of Xantrex XW6048 inverters. Your advice 
would be welcomed. 

 

* The system must be split phase 120/240, not 3 phase. 

 

* Outback seems "out" because the inverter group should handle backup battery 
recharge using grid or generator AC...and we also want to sell excess PV power 
to the grid.

 

* No cobbled together AC coupled systems would be considered without a 
convincing way to feather the end of charge on the battery when the grid is 
down...float & all. I don't want to go back to the days of clunky, coarse 
battery "end of charge" care. 

 

* Sunny Island/Sunny Boy is in contention but I'm not keen on having to stack 
in pairs to maintain the 120/240 three wire architecture. A single Sunny Island 
failure would take down two of the yellow boxes. What is the limit on 
stack-ability for Sunny Island?

 

* A battery sales rep suggested Satcon brand but I think that's bogus advice. 
Satcon is pure grid intertie only, right?

 

***********************************************

 

So...there is your challenge de la semaine (challenge of the week). Who builds 
an inverter system with Xantrex XW-like features only bigger...much bigger? OR: 
who could supply the "Mother of Sunny Island/Sunny Boy" system? Replies would 
be welcomed on the  List or off.

 

The Wrench List is the Bomb!

 

Mick Abraham, Proprietor
www.abrahamsolar.com

Voice: 970-731-4675
 
-----Inline Attachment Follows-----

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


 
-----Inline Attachment Follows-----


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




      
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to