Rather than use 3" pipe for the run, you could use reducing bushings in a 3" LB and use it with a 2 1/2" conduit.

At 12:47 PM 8/14/2010, you wrote:

The lesson was that even if, say, for a 2 ½ “ conduit says three 350 MCMs are OK, that doesn’t mean that a 2 ½” LB I was planning on using is rated for three 350s.

For the first time ever I saw printed in the LB itself the specified max conduct size, in this case 4/0 for a 2 ½” LB.

So for this short conduit run I upsized everything to 3”.

I looked at the Thomas and Betts spec sheet kindly supplied by Ratico on their LB offerings and there was no notation of max conductor sizes that I could find.

marco

Marco,
I'm curious to know what you did after the "hard" lesson. Was it an issue of difficult/impossible installation, or an AHJ issue? It seems like the most straightforward solution in a situation like this is to replace your conduit bodies (LBs in this case) with a larger size, and then install reducers in order to leave the existing conduit runs intact. I'm looking at an upcoming installation where I would like to use 1-1/4" EMT, but will need 1-1/2" conduit bodies to be ok with wire fill.

-Hans


----------
From: [email protected] [mailto:[email protected]] On Behalf Of Marco Mangelsdorf
Sent: Thursday, August 12, 2010 8:19 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] Aluminum conduit LBs
Anyone know where I could go to find out the max conductor sizes that threaded Al. LBs can handle?

I learned the hard way that a conduit of X inches that can handle conductors of a certain size does not necessarily mean that a LB of the same diameter can handle the same size conductors.

Thanks,
marco


No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 9.0.851 / Virus Database: 271.1.1/3067 - Release Date: 08/12/10 08:34:00
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
NABCEP TM  Certified PV Installer
Office - 740-448-7328
Mobile - 740-856-9648  
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to