Wire gauge isn't the only consideration.  Check all crimps and connections in 
the DC path.  A bad one can cause more drop than the wire.

Dan


--- On Fri, 8/20/10, Jeff Oldham <[email protected]> wrote:

From: Jeff Oldham <[email protected]>
Subject: Re: [RE-wrenches] Voltage discrepancy
To: [email protected]
Date: Friday, August 20, 2010, 3:43 PM

boB - it is 4' of #6 CU. and the charge rate averages 45A @ 12V nom. I 
understand that the Vd diff. from 13.6V @ 15A and 14.2V @45A is .1V but the 
meters when set nuts on at 14.2V are off by at least .3V @ 13.6V. This is not 
wire sizing issues nor does that explain the calibration drift over a few days.


>From the Solar, Wind and Hydro powered office of Jeff Oldham/Regenerative 
>SOLutions




      