Darryl,

A GFCI will work without an equipment ground connected to it.  That is why the NEC allows a GFCI to be used as a replacement for a two-wire plug.  But in an ungrounded power system a GFCI will not work unless there is a low impedance between neutral and ground.  For a small ungrounded power system such as portable generator with no neutral ground bond, a GFCI won't trip because there is too much impedance between neutral and ground.

Kent Osterberg
Blue Mountain Solar



Darryl Thayer wrote:
Just a note, FYI
The GFCI will work without a ground, it operates when the current is different between the Hot and the Neutral

If the generator does not ground the neutral it is supposed to be grounded on the service or what ever is using the power.  The honda inverter generator may not have any conductive surfaces.  Indeed I would like to see a ground on the neutral and the generator frame connected together.  Here in MN we had an accident where a person was killed touching a generator frame. 

The buck boost transformers I use a lot are the 120-240 (or 208)  they are usually about 1kW they have an Output of 16 or 32 volts the secondary is put in series with the line and either bucks or boosts the voltage.  If for example you had 120,240 you would put each 120 on each primary and the neutral would be the common connection.  If the secondary was connected to buck, you would have 240 -32 = 208 volts.  the neat thing about it is that a 1 kW buck boost can produce power for 7.5 kW approximately.  So the Buck boost transformer only carries about 1/7 the load,  and you need a 1/7 the kW in the transformer that you need in the generator or the inverter.  In your case if the gen is about 3.5 kW you couls use a 500 watt Buck boost. 

Darryl

 

--- On Thu, 8/19/10, Brian Teitelbaum <[email protected]> wrote:

From: Brian Teitelbaum <[email protected]>
Subject: Re: [RE-wrenches] DR2424 inverters charging poorly: three units in two days!
To: "RE-wrenches" <[email protected]>
Date: Thursday, August 19, 2010, 10:03 PM

Kent,

 

Thanks for that info.

 

Have you tested for voltage between the L1 and ground while the generator is running, or just tested for continuity between neutral and ground when not running?

 

I wonder how much Honda paid the City of LA for that sticker J

 

Brian Teitelbaum

AEE Solar

 

From: [email protected] [mailto:[email protected]] On Behalf Of Kent Osterberg
Sent: Thursday, August 19, 2010 7:51 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] DR2424 inverters charging poorly: three units in two days!

 

Brian,

I also have observed that the Honda EU1000i and EU2000i inverter generators do not have a neutral-ground bond.  Considering that they are intended as a portable power system and have a three-prong plug it does seem strange that there is no bond.  There is also no GFI protection which is normally required for 15 and 20-amp outlets on portable generators.  But then a GFI wouldn't work without a neutral-ground bond anyway.  There is no sign of a UL listing, but mine has a sticker from the City of Los Angeles saying that it is "approved for use".

Kent Osterberg
Blue Mountain Solar


Brian Teitelbaum wrote:

Mick,

 

Raising the engine RPM will also increase your frequency above 60Hz, which could injure any electronics running in the house, so be careful there.

 

Allen,

 

You mentioned that the inverter/generators have no bond between the neutral and the frame. I don’t see how they can get away with that and still have a three-prong receptacle on the unit. Since these are designed to be portable gennies, they represent a complete power system, able to directly run loads, and therefore must have a bond. Maybe they don’t have any kind of over-current protection on them, and if there is no breaker to trip, the bond is not needed, and they can get away with that. I haven’t had a chance to play with any of those enough to look that closely. Are you sure that there is no bond? If so, then this makes them ideal for small off-grid back-up gennies, on top of the many plusses I knew about.

 

Brian Teitelbaum

AEE Solar

 

From: [email protected] [mailto:[email protected]] On Behalf Of Mick Abraham
Sent: Thursday, August 19, 2010 5:20 PM
To: [email protected]; RE-wrenches
Subject: Re: [RE-wrenches] DR2424 inverters charging poorly: three units in two days!

 

I knew Allan S. & Brian T. would be among the first to chime in with helpful observations. My recollection, however, was that prior efforts with portable generators had worked OK with DR sets...and I know of one setup like that which is working OK in my home county for sure. (That's a portable with fairly big wattage rating, however.)

 

 I increased the engine RPM on that newly repaired generator but I felt creepy around 125 volts per leg. No more fireworks, please, but should I tweak it up faster?

 

So...Allan is saying that he suspects these DR units are operating "normally" and therefore could not be helped by a repair. I look forward to receiving additional posts on this topic. 

 

****************************************

 

Brian T's point (about the neutral usually being bonded to metal frame on portable generators) is well taken. I tried to buzz it out with my continuity meter and read "open" between genset neutral & metal chassis. This was at the end of some hot & hectic overwork, however, so maybe I screwed up on that test...loose meter cable or sketchy switch position on the meter,  maybe. I will test that again next time. 

 

Although it's a portable genset of fairly low price, I think it has some fancy electronic ground fault interrupter or maybe even electronic ground switching. Perhaps that's why it wouldn't buzz out when the engine was off. When the "green wire" on the twist lock power cord was connected to the metal of the Power Panel System--as seems quite reasonable--the generator's voltmeter would drop to zero as soon as the twist lock plug was inserted. That's when they called me...to boldly go where no normal, sane electrician ever would. I loosened off that green wire from the Power Panel and all looked well. I should have stopped there. The manual for the generator was no help at all. 

 

Three poorly charging inverters in two days...plus one Big Bang...that was not one of my better weeks! 


Mick Abraham, Proprietor
www.abrahamsolar.com

Voice: 970-731-4675


On Thu, Aug 19, 2010 at 6:00 PM, Allan Sindelar <[email protected]> wrote:

Mick,
You have missed one fundamental point: The DR (and earlier Trace mod-square series) gulp only the peak of the AC supply waveform when charging. They need 164V AC at the peak of the waveform at rated charging load to supply full rated DC current. A small dip in AC peak voltage results in a disproportionate loss of DC charging current. You identified the source of the problem when you identified the gennies as portable units. Cheap generators provide a 120V AC RMS voltage, but the waveform is flat, with a low peak, especially under load. This is described somewhere in the DR manuals, I think.

The best solutions we have found are the inverter/generators, from Honda, Yamaha, and now others. Perfectly synthesized sine waveforms and good DR performance.

Cheap generators are no bargain.
Allan

Allan Sindelar
[email protected]
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com


On 8/19/2010 5:48 PM, Mick Abraham wrote:

Greetings, Mechanics~ Please review my problem du semaine and chime in if you are so inspired. 

 

My prior experience with the DR series Trace inverters could be summed up in two words: practically bombproof! 

 

(There was one time...way back in the day...when a barely broken in unit stopped charging with adequate amperage, and...thinking...there was some screwy behavior on the LED indicators and maybe something else. That issue was resolved under warranty and was declared by Trace tech support to involve the "triacs".)

 

Last month I visited two customer sites right after one another. Site #1 has a single DR2424, 120  volts from the portable generator, transferred fine...no problems...but would only deliver a puny five amps to the battery, regardless of tweaks to the "battery size" & "charge rate" knobs.

 

Site #2...the very next day...has twin DR2424 units, similar OK voltage from the portable genset, similar normal seeming behavior, series stacking cable in place, but a similarly puny DC amperage delivery to the battery. This pair was slightly higher on DC amperage...about 7 amps per unit. Tweaks had no effect. 

 

********************************************************

 

In fairness to Site #2, some weeks prior...the genset had been newly purchased and would not maintain output AC when connected to the inverter pair. I inherited a new set of customers when nobody else seemed to know what to try. I ungrounded the generator plug connection and things took off...and the charging amps were A-OK. Then...as a good safety minded technician...I grounded from the metal ground lug on the frame of that generator to the client's ground rod and the otherwise routine service call became much more exciting. 

 

BANG-I fried something in the generator...voltage regulator, maybe. Then I remembered why I try to never help out on equipment purchased elsewhere. I broke my own rule...

 

After an intense conversation with the generator supplier, the service guy agreed to fix the genny--"one time and never bring it back". When it came time to re-connect the repaired generator, my new customers wanted me to be there. I thought that would all be ho-hum so long as we left the frame ungrounded but then I observed the low charger performance. Now I suspect that something about the generator flame-out also blew important items in the inverter pair. 

 

*****************************************************

 

I'm writing the Wrenches to ask:

 

Can anyone point to the likely problem on these three machines?

 

I probably can't fix this myself but perhaps could be encouraged to try...somebody on Ebay is selling "FET boards" for the DR2424 inverter. Inspiration, anyone.

 

Failing a local repair, does anyone remember the flat rates for repairs by the authorized fix it shops?

 

OR: if any List participants have a matching inverter in inventory...or two...or three...perhaps they could contact me off list with pricing, etc. Neither client is likely to have the cash for new TR-2424 inverters.

 

Oh, yes...if any could offer a Big Bang theory, that would help with my education. The neutral on that portable generator is isolated from ground, so the metal frame should be a non-participant in any electrical activity on the AC side of things. The metal frame is...thinking...connected to the negative of the 12v cranking battery so maybe that's a clue. The ground rod to which I connected is also connected to the negative of the 24v house battery and also is connected to AC neutral from the Trace Power Panel. 

 

Thanks all around. The Wrench List is the Bomb, but with no loud percussive effects!


Mick Abraham, Proprietor
www.abrahamsolar.com

Voice: 970-731-4675

 
_______________________________________________




_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]