Hi Nik, Some questions:
Is this a 3 phase service? Details on the UPS; brand, kVA, age? Breaker sizes for the circuit(s) supplying the UPS and fan? Details on the air conditioning system and fan. Are they powered through the UPS? Dick Ratico Solarwind Electric --- You wrote: Wrenchers, We installed our first SunnyBoy 8000 this month. The customer (happens to be electrical engineer) is complaining that their computer UPS systems are tripping whenever the air conditioner (with 120V fan) comes on. This didn't happen before commissioning the solar system and it doesn't happen when the inverter is disconnected. So, of course, they suspect the inverter is the culprit. The theory being that the inverter itself is going out of phase when one of the legs is loaded down momentarily. So far, SMA tech support is not agreeing. They are blaming the problem on the unbalanced loads and/or the UPS systems. Their latest solution is to move the UPS systems to the other leg. Not surprisingly, the customer is not impressed with this game of Kick the Can Down the Road. The inverter does not drop the grid, nor display any error codes when this happens. This is a 200A, 240V service. The 120V fan draws about 10A continuously, 40A surge. Anybody else with similar experiences? Suggestions? Thanks Nik -- Nicholas Ponzio NABCEP Certified Solar PV Installer Building Energy 1570 South Brownell Road Williston, VT 05495 t: 802-859-3384 x15 f: 802-658-3982 c: 802-365-1973 http://www.BuildingEnergyVT.com _______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org --- end of quote --- _______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org

