One clear advantage of micro inverters is that string size is not an issue. Especially, dealing with ULA racking, where modules go up in groups of 4, often good string sizing is not available. Sometimes string sizing can be found at the bottom of the hot weather voltage window for string inverters. Using minimum voltage may become a problem a few years down the line when the modules degrade. We may also see warmer weather, as we have gone beyond the 350 PPM trigger point in atmospheric carbon (385 PPM). Micro inverters should bypass these issues.

Also on a ULA ground mount system, inverters can be replaced without removing modules.

At 09:44 AM 9/5/2010, you wrote:
Thanks for the discussion, I have found that for me there is no time advantage in micro inverters. The wire management under the modules slows me down. But for very small systems they seem to advantages. The industry is rapidly changing, and with the code 2011 NEC and the arc fault protection clause, it will be a game changer with module optimizers and microinverters taking the lead.
Darryl

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to