That looks like a tin plated aluminum lug (aluminum corrosion) with a plated steel screw (rusted screw).......
Here is an explanation of the differences between both ILSCO GBL 4 lugs from John Wiles Code Corner in Homepower issue 102 "The Ilsco GBL-4DBT is a lay-in lug
made of solid copper, which is then tin-plated. It has a
stainless steel screw to hold the wire. The lug accepts a #14
(2 mm2) to #4 (21 mm2) copper conductor. It is listed for
direct burial (DB) and outdoor use and can be attached to
aluminum structures (the tin plate). The much cheaper Ilsco
GBL-4 lug looks identical, but is tin-plated aluminum, has
a plated screw, and is not listed for outdoor use."
Jamie Johnson
NABCEP Certified Solar PV Installer #031310-118
General Manager
SOLAR POWER ELECTRIC
EC13001765
|
![]() |
_______________________________________________ List sponsored by Home Power magazine
List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org