On my own system I have a DC suppressor from
http://www.surgesuppression.com/

It's UL listed with a 25-year warranty. Not as cheap as a Delta (or Citel as far as I know) though, but I felt a lot more confident with this given our crazy lightning storms in FL.

DKC

-------- Original Message --------
Subject: Re: [RE-wrenches] Delta LAs
From: Mick Abraham <[email protected]>
To: RE-wrenches <[email protected]>
Date: 2010/9/14 15:17

Citel products do have a listing mark but this is European style CE, not
American style UL/ETL. Citel is reputedly working on American
certification but one would be advised to not hold one's breath.

The Citel products which mount to a DIN rail have an LED indicator which
goes dark once the surge elements have been sacrificed. Also some of
their units have an auxiliary switch which can remotely indicate a blown
condition. This is in the form of dry contacts..a normally open and a
normally closed one, so various indicator circuits can be designed
around that. The contacts have a low amp AC rating and also a (lower
amp) DC rating but I do not remember the numbers at present.

Jolliness,

Mick Abraham, Proprietor
www.abrahamsolar.com <http://www.abrahamsolar.com>

Voice: 970-731-4675


On Tue, Sep 14, 2010 at 12:43 PM, R Ray Walters <[email protected]
<mailto:[email protected]>> wrote:

    You could buy several ground rods for the cost of one Delta.
    Ground Impedance is the real issue. Both the Delta and the
    Polyphasor need a good ground to work.
    While I haven't seen much of a correlation between Deltas and
    reduced lightning damage, (lots of system damage with and without)
    I have found that well grounded systems (tied to a steel cased well)
    have never had a problem, even with direct strikes to a wind turbine
    (did lose the $40 turbine rectifier, but nothing else)

    I now own a clamp-on ground impedance tester, and the results were
    miserable. Some electrodes were over 800 ohms to ground! (code
    requires under 25 ohms)
    I'd spend more time and money reducing ground impedance, and then if
    it makes you feel good inside, throw the little "lightning faeries"
    in, if the AHJ isn't looking.......

    If its really lightning country, and a really expensive off grid
    system, I use Polyphasor, but they have their own issues. (very
    expensive, no UL listing, loose internal connections, nuisance
    tripping, need a large J-box to mount them inside, etc.)
    I haven't tried the Citel stuff, but it looks to be listed, and
    mounts on a DIN rail. After installing a couple hundred Deltas, I'd
    try something else at this point.


    R. Walters
    [email protected] <mailto:[email protected]>
    Solar Engineer




    On Sep 14, 2010, at 10:22 AM, Kristopher Schmid wrote:

    My thought here is that nothing will protect the equipment from a
    direct strike, but a near strike that may induce a significant
    surge may be absorbed by the LA and protect the equipment.  I like
    the feedback so far.  It would not break my heart to stop using
    them altogether.:-}
    Kris

    Legacy Solar
    864 Clam Falls Trail
    Frederic, WI 54837
    715-653-4295
    [email protected] <mailto:[email protected]>
    www.legacysolar.com <http://www.legacysolar.com>

        -----Original Message-----
        *From:* [email protected]
        <mailto:[email protected]>
        [mailto:[email protected]
        <mailto:[email protected]>] *On Behalf
        Of *August Goers
        *Sent:* Tuesday, September 14, 2010 10:39 AM
        *To:* RE-wrenches
        *Subject:* Re: [RE-wrenches] Delta LAs

        All -
        I guess my thought is a little off topic, but are lightning
        arrestors even worth using at all? My logic has always been
        that if lightning does indeed strike that it's likely going to
        blow the arrestor and and inverter. We don't have much of a
        lightning issue issue in the Bay Area so I don't have any
        direct experience.
        Best,
        August

        On Tue, Sep 14, 2010 at 6:29 AM, Kristopher Schmid
        <[email protected] <mailto:[email protected]>> wrote:

            It is quite ironic that just a week after I posted a
            question to the group
            on testing the integrity of lightning arrestors, I had one
            apparently faulty
            out of the box.  The manifest of this was interesting:
            when the AC LA
            (LA302R) was connected in parallel on the AC input to a
            SB3000 inverter,
            there was 125vac neutral to L1, 125vac neutral to L2, and
            1Vac L1 to L2.
            SMA tech support suggested the LA as the issue and sure
            enough, it was.
            Attempting to test good and faulty arrestors with an
            ohmmeter gave the same
            result - off scale open.

            Any thoughts or comments from the group?

            Kris Schmid

            Legacy Solar
            864 Clam Falls Trail
            Frederic, WI 54837
            715-653-4295
            [email protected] <mailto:[email protected]>
            www.legacysolar.com <http://www.legacysolar.com/>

            _______________________________________________
            List sponsored by Home Power magazine

            List Address: [email protected]
            <mailto:[email protected]>

            Options & settings:
            http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

            List-Archive:
            http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

            List rules & etiquette:
            www.re-wrenches.org/etiquette.htm
            <http://www.re-wrenches.org/etiquette.htm>

            Check out participant bios:
            www.members.re-wrenches.org
            <http://www.members.re-wrenches.org/>




        --
        August Goers
        VP, Engineering

        Luminalt Energy Corporation
        1320 Potrero Avenue
        San Francisco, CA 94110
        O: 415.641.4000
        M: 415.559.1525
        [email protected] <mailto:[email protected]>

    _______________________________________________
    List sponsored by Home Power magazine

    List Address: [email protected]
    <mailto:[email protected]>

    Options & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>



    _______________________________________________
    List sponsored by Home Power magazine

    List Address: [email protected]
    <mailto:[email protected]>

    Options & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>





_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options&  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules&  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to