Marco, In this case, slightly differing resistance between your grounded and ungrounded conductors will not make any difference. You will just need to do your DC voltage drop calculations for each half separately, instead of the typical voltage drop calculation that uses wire length x 2. Different resistance in parallel battery cables is an important issue, but that's not what you're talking about. Regards, -Hans
_____ From: [email protected] [mailto:[email protected]] On Behalf Of Marco Mangelsdorf Sent: Monday, September 20, 2010 11:08 AM To: 'RE-wrenches' Subject: [RE-wrenches] fewer wires, mo bettah? Check this out. Four series strings of mods on a same plane roof feeding a larger Sunny Boy or Fronius inverter. Four #10 conductors for the ungrounded, fused (at the inverter) conductors. And for the grounded conductor, a single, common, larger conductor from those four strings. So instead of four pairs of wires, or eight total, I'm using just five (plus ground). Assuming that the larger grounded conductor is adequately sized taking into account conduit fill and temp derate for exposed conduit, does anyone see a problem in doing this? I've already been doing this for several years with no problems that I can tell. But it occurred to me whether different resistances between the ungrounded conductors and the grounded conductor might be an issue. Feedback appreciated. Thanks, marco
_______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org