Allan,
A very simple way to do this is install a float in the tank you are pumping to 
with a shutoff valve controlled by the float. Install a Square D pressure 
switch with a DC rating by the pump. As the float rises to full in  the tank 
and chokes off the discharge outlet the pressure in the line will rise and trip 
the pressure switch. We are using this method exclusively as there seems to be 
a glitch in the high frequency communication between the SQ Flex and the CU 200 
controller.  The pump is not shutting off on command from the controller 
consistently in stand alone applications. I am aware of  a half  dozen of these 
systems experiencing this issue. 
You might install a small pressure tank in the line to avoid water hammer in 
the system. Simple and cheap.
Nathan Jones
Power Source Solar Inc.
Springfield, MO
417-833-4274

On Fri Oct 15th, 2010 3:10 PM CDT Allan Sindelar wrote:

>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches@lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
>



      
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to