Thanks Guys, Here's an update for anyone who cares. The specifics I was looking for are included in IEEE 1547.1, which is inherently included in UL 1741. In other words, since 2007, if you have an inverter listed to UL 1741, it must also meet (by certification) the requirements of IEEE 1547 and 1547.1. In fact, the sections of UL 1741 that formerly applied to the Utility Compatibility functions have been removed. Voido. They are now replaced by IEEE 1547 & IEEE 1547.1. IEEE 1547.1 is clear and precise about the production test requirements I was looking for. UL 1741 is weak on the issue. In general, utility companies rely on IEEE documents and requirements for their guidance. I see why some of them require field verification of the non-islanding function by flipping the AC switch off with the inverter running... Well, not exactly. Technically, the non-islanding function is something else. The "Cease-to-energize" function is what they are actually verifying in the field. Here's a short rundown on the issue.... IEEE 1547.1 (Clause 6; Production Tests) requires production tests for response to abnormal voltage, response to abnormal frequency, and synchronization. Combined, these would constitute production testing that confirms the non-islanding functions that are Type tested on a sample unit. And there's more. This section also requires that the documentation of these production tests be provided with the equipment. IEEE 1547.1 (Clause 7; Commissioning) requires some verification and testing steps. These are allowed to be performed by a qualified person and the utility may require that they witness the process (at their option). Inherent to this section is a requirement that there be a commissioning report generated which contains data related to the process. "A commissioning test report shall be produced and shall contain the results of all tests and a listing of the final ICS settings." The required steps involved in Commissioning include: Verification and Inspection, Identifying any required Type and Production tests that were not performed and performing them in the field; Unintentional Islanding functionality test; Cease-to-energize functionality test; Documentation of revised settings. Understand that all of these steps are REQUIRED AS PART OF THE COMMISSIONING PROCESS, per IEEE 1547.1. My focus is primarily on the Commissioning procedure... I'll skip the inspection and verification steps for this post. Note that Clause 7.3 of the Commissioning section requires field performance of any Type or Production tests that have not been performed. When the manufacturer fails to include the Documentation of Production Tests with their product, the commissioning technician has no choice but to do them in the field. (NOTE TO INVERTER MFRS: INCLUDE CLEAR DOCUMENTATION OF YOUR PRODUCTION TESTS WITH EACH INVERTER, PER IEEE 1547.1 Clause 6.4; NOTE TO INSTALLERS: HAVE THIS DOCUMENTATION HANDY AND LEAVE IT WITH THE INVERTER.) Clause 7.4 is the Unintentional Islanding functionality test. If the unit is connected to the grid via reverse-power or minimum-power protection equipment (commonly referred to as non-export or zero-export; relatively rare) instructions are given for testing. This test is waived if the inverter is certified to Clause 5.7, the Type test for Unintentional Islanding. (Check) If the unit is not certified to 5.7 and not connected via zero-export protection equipment, this function is to be tested according to procedures provided by the integrator or the manufacturer. UL 1741 Listed inverters should be certified to Clause 5.7, which makes them eligible for the waiver. Clause 7.5 is the Cease-to-energize functionality test. This tests that the inverter does not energize the output (AC) terminals on loss of grid AC. It also checks that the restart/reconnect time delay (5-minute wait) functions as required. The test is simple. Run the inverter at any power level and open the ungrounded AC phase conductors. Verify that the output terminals of the inverter are not energized. Apply AC power. Verify that the unit waits the required amount of time to reconnect. There are two important sentences in this Clause to know about. The first is that "An ICS that meets the requirement so 5.9 (open-phase type test) and 7.4.1 (zero-export) satisfies the requirements of this subclause." This means that a UL 1741 Listed inverter interconnected via zero-export equipment is exempt from this test. The second sentence to know about is this one: "The following procedure may be adjusted dependent on an agreement between the area EPS authority (electric utility) and the system installer." This means that, every time the utility does not require you to test this function, they are agreeing to "adjust" this procedure, even if they don't tell you they are. You are getting a free pass. Let me repeat that another way... IEEE 1547.1 REQUIRES that this test be done unless the above-mentioned exemptions are met. As an installer, you must be prepared for and expect to do this test. Nowhere in the Commissioning section of IEEE 1547.1 does it exempt performing the Commissioning steps or producing the Commissioning test report. I am of the strong opinion that having the manufacturer's Production Test Documentation on-hand will go a long way toward gaining the utility's acceptance of the system without performing the Cease-to-energize functionality test. I believe that most of our modern inverters will meet one of the exceptions to the Unintentional Islanding functionality test. I believe that it is best practice to perform comprehensive commissioning on all systems, and record the relevant data. I have always found that doing this and having your documentation together gains respect from AHJs and utility inspectors. I believe that by doing this, we demonstrate professionalism and responsibility. Working with utilities in a manner that demonstrates professional, knowledgeable, and responsible behavior can only benefit our respective organizations. Happy commissioning! Matt Lafferty _____
From: [email protected] [mailto:[email protected]] On Behalf Of Exeltech Sent: Tuesday, October 19, 2010 12:20 PM To: RE-wrenches Subject: Re: [RE-wrenches] Inverter 1741 Listing Process boB covered the main points perfectly. Manufacturers of UL-certified products are subject to unannounced spot-checks several times a year by the issuing NTRL to verify the products coming off the production line are absolutely identical to the products submitted for UL testing. Any major deviation in the production units from lab-tested units can result in immediate de-certification and possible recall of any affected product(s). "Major" in this case could be different software, mechanical changes, or a substitution of any components that affect safety or unit operation in any manner with unauthorized components .. for openers. By the way .. for anyone who's not met boB in person .. I had the good fortune to do so at the Midwest Renewable Energy Fair in Wisconsin this past June. Great guy. Dan --- On Tue, 10/19/10, boB Gudgel <[email protected]> wrote: From: boB Gudgel <[email protected]> Subject: Re: [RE-wrenches] Inverter 1741 Listing Process To: [email protected], "RE-wrenches" <[email protected]> Date: Tuesday, October 19, 2010, 12:42 AM On 10/18/2010 9:53 PM, Matt Lafferty wrote: Thanks for the info Dan and boB. What production tests required to maintain listing? Do you happen to know if there is a different regimen for micro vs string vs central inverters? You mean, a difference between the two when UL, ETL, CSA comes by for their pop inspection ?? Off hand, I don't see why one inverter would be given any different kind of attention than the other type. The UL/ETL followup inspections are basically to make sure you are following the proper manufacturing and testing processes such as, software version, verification that you are using UL recognized sources of parts and materials, hi-potting at the correct voltages, etc. They are both grid-tie inverters so the testing processes are very similar. I'm sure that Dan will pick up on anything important that I forgot. boB I'm working on developing a detailed commissioning procedure. Detailed yet generic. There will be at least two versions for inverters. One for string and one for central. In my book, central inverters have re-combiners (standalone or integral) and string inverters don't. I'm trying to understand which functions are tested in the factory on every unit so I can avoid unnecessary duplication by the commissioning people. Thanks in advance for any light you can shed on the subject! Matt Lafferty _____ From: [email protected] [mailto:[email protected]] On Behalf Of Exeltech Sent: Monday, October 11, 2010 10:04 AM To: RE-wrenches Subject: Re: [RE-wrenches] Inverter 1741 Listing Process Matt, The 5-minute delay is verified in the group of inverters sent to the test laboratory. Then, as long as the software and hardware don't change, it's presumed the delay in all production units meets the value(s) measured in the tested units. An alteration in either hardware OR software can result in a unit being required to completely re-test (as Bob pointed out). NRTLs get copies of the source code and can and do periodically compare their copy as submitted with the original test units to the software being programmed into the inverters during production to verify it's the same. NRTLs conduct unannounced "field audits" by simply showing up on site and randomly selecting various aspects of the product for verification -- including the software. The overall UL1741 certification process is extremely complex, very time consuming, and quite expensive. Dan --- On Fri, 10/8/10, boB Gudgel <[email protected]> wrote: From: boB Gudgel <[email protected]> Subject: Re: [RE-wrenches] Inverter 1741 Listing Process To: [email protected], "RE-wrenches" <[email protected]> Date: Friday, October 8, 2010, 9:26 PM On 10/8/2010 6:04 PM, Matt Lafferty wrote: Hola Wrenches, Does anybody know off the top of their head if the "5-minute-wait-to-interconnect" function is tested on 100% of inverters produced? (i.e. every single inverter is tested with AC & DC within the start parameters of the unit for at least 5 minutes) Thanks! Matt Lafferty Good question. I bet it's not 100% tested because if the software does not change, then they may just not wait the extra 5 minutes in order to save money on testing. Or, maybe they do a random sampling for this test. Theoretically, it shouldn't matter as long as the software does not change and the hardware is tested enough in other ways, like, timers and clocks etc. BTW, Nowadays, there are two options for manufacturers of grid interactive inverters.... And the UL spec has gotten more stringent. One option is that you have to have the code (software) blessed by the NRTL in a separate process (another UL specification, (UL 1998 -Software in Programmable Components") OR, if they don't go for that option, then if software changes need to be done to the inverter, the inverter must (technically) go through the UL1741 listing process all over again. boB
_______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org