Thanks for the recommendation. Yes, 30w. These are outdoor fixtures with many 
1w or 3w LEDs. 

Yup. Lots of calcs ahead to deal with different runs. 

Jason Szumlanski

On Oct 26, 2010, at 7:52 PM, "Darryl Thayer" <[email protected]> wrote:

> Battery to distubution, I would use a T fuse and a battery breaker to shut 
> off the distubution panel.  
> I would distubute with a Sq.D QO panel. I believe the max breaker size for DC 
> rating is 60 amps on QO breakers.  
> 
> Do you mean 30 watt or 30 watt equivelent leds?  the 30 to 50 watt led is 
> very large.  
> 
> do your voltage drop calculations, to determine wire size.  
> DT   
> 
> --- On Tue, 10/26/10, Jason Szumlanski <[email protected]> wrote:
> 
>> From: Jason Szumlanski <[email protected]>
>> Subject: [RE-wrenches] Small Scale DC Lighting Distribution
>> To: "RE-wrenches" <[email protected]>
>> Date: Tuesday, October 26, 2010, 5:51 PM
>> We have an opportunity to do two
>> small scale 24Vdc lighting systems at
>> an off-grid location run off PV and batteries. We're
>> talking maybe 8-12
>> LED fixtures drawing 30-50W each (on motion sensors).
>> However, we might
>> want to plan for future expansion. Question: what are you
>> doing for DC
>> distribution in cases like this? I am considering a Midnite
>> DC
>> disconnect box with DIN rail mounted DC breakers.
>> Otherwise, I might go
>> with a class T fuse and holder with a Square D QO load
>> center.
>> 
>> In each case I am looking at a small battery bank and
>> appropriate PV
>> with a Morningstar controller. Any thoughts on PV circuit
>> protection?
>> 
>> The system we are replacing is kind of sad, using inline
>> automotive
>> fuses and a lot of exposed wiring. Ultimately, it would be
>> nice to have
>> a flexible but completely integrated system.
>> 
>> Jason Szumlanski
>> Fafco Solar
>> 
>> _______________________________________________
>> List sponsored by Home Power magazine
>> 
>> List Address: [email protected]
>> 
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out participant bios:
>> www.members.re-wrenches.org
>> 
>> 
> 
> 
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org