Howie,

In an ac coupled system with Outback inverters you could use a diversion controller such as a Morningstar Tristar 60 on the dc side. That would allow using an ac coupled system and a nicely controlled finish charge for the batteries too. Since there is already a MX60 to do the finish charge in the system you are considering, a voltage controlled switch, like the Morningstar relay driver, could simply shut down the SB3000.

Kent Osterberg
Blue Mountain Solar


Howie Michaelson wrote:
Hi All,

I have done several AC coupled off-grid systems using Sunny Islands and
Sunny Boys, but I am now doing one with a dual stacked OB VFX3648 (with a
PSX240 on the Inverter out for load balancing) and a SB3000.  There is
also an existing array that is running through an MX60.  What I am
wondering about is how folks have set up AC coupled string inverters to
best utilize the solar gain while not toasting the batteries.  I'm a big
fan of the tapering control offered by SMA through the frequency shift of
the SI's, but that's not available here.  What relay/contactor setup have
folks found most efficient and safe?  Thanks in advance,

Howie