Gilligan,

Below is the data you asked for:

A) Measure and Record DC Voltage between Positive and Negative (VOC). 0.0 to 0.1 B) Measure and Record DC Voltage between Positive and Ground. 0.0 to 0.1 C) Measure and Record DC Voltage between Negative and Ground. 503 VDC

No sign of rain.

No evidence of a ground fault. If a fault exists, it is intermittent. The system worked fine for a week with the new inverter. Since it went down, I've done repeated checks and found no evidence of a fault. Fortunately the system is close by.

There is one string of 10, Sanyo 210s. The installation is 9 months old. The only J-Box is in the attic and is dry and wired very cleanly. The system worked great until a few weeks ago.

I will check the rotation of wheel on the meter again, when we get the GFP fuses in. I think the inverter was producing power.

No Spark on the DC wires.

Note:  The first inverter did NOT blow the GFP fuse.  I worked intermittently.

Has anyone had problems with Sanyo modules faulting?

Thanks,

Drake


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to