Colleagues:

I had posted earlier that I was having problems reliably starting a particular generator using an Outback Mate. My resolve was to determine conclusively if the Outback mate was at fault or if I could trust it in the future. I installed a data monitoring system to check battery voltage, gen start signal and gen AC waveform and briefed the care taker and staff to scrutinize the system carefully during the test period. Here are the results:

There were 4 generator start failures over a period of about 4 weeks. Failure numbers 1 and 3 were verified to have been caused by the generator. Failures 2 and 4 were due to failure of the customer to reset the Mate after failures 1 and 3. This was a training error that was partly mine. No failures can be blamed on the Outback equipment.

Moral of the story: Generator start systems are complicated. You need to know your generator and your customer needs to know his or her Mate. But, the Mate AGS works.

More information:

The Kohler RES 15 displays numerals under normal circumstances and alpha characters under abnormal circumstances. I posted a note in the generator shed informing anyone that if alpha characters are seen, to note the characters, time, date and then to call me.

The Mate is difficult enough for the technician to understand. My customer has an elderly caretaker for whom English is a second language. After I discovered the training error, I created a few flip charts with lots of graphics and copies translated into Spanish, followed up by on-site training. This should prevent repeats of the failure to clear AGS Errors. This highlights the industry wide problem of systems having too complicated a front end.

Data monitoring proved the point that generator failure was the original culprit. If anyone is interested in more information about a roll-your-own low-budget data monitoring system, I created a page on the subject: http://millersolar.com/case_studies/Data/data.html

I firmly believe that third party generator start hardware adds an unnecessary level of complication and removes the added feature of tieing generator stop to the float stage. I will continue to use and recommended the Outback integrated AGS system.

William Miller




Please note new e-mail address and domain:

William Miller
Miller Solar
Voice :805-438-5600
email: [email protected]
http://millersolar.com
License No. C-10-773985
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to