Bill,

You stated below that a starwasher installed with an Ilsco lay-in lug violates 
the listing of the lug.  Can you point me to where this is in writing, or does 
one have to purchase the UL standard?

Best,
Jerry Caldwell

--- On Sun, 9/12/10, Bill Brooks <[email protected]> wrote:


> Finally, many of the module manufacturer's installation
> manuals, the ones we
> are supposed to believe, actually violate the listings of
> the products they
> recommend. The ILSCO GBL-4DBT lay-in lug is the most famous
> example of these
> mistakes. Several prominent installation manuals state that
> a stainless
> starwasher must be installed under ILSCO lug. Although this
> will work, it is
> a violation of the listing of the lug. Yet it is in the
> installation manual
> and it is one of only a very few options--and it is wrong.
> What are we to
> think of this whole situation? It is out of control and
> messed up.


      
_______________________________________________