Did he ask to see the UL sticker on the batteries too?


On Monday, November 29, 2010 5:07pm, "Philip Boutelle" <[email protected]> 
said:

Wrenches,


We have a string of batteries being inspected by a local AHJ. In plan-check 
comments, I was asked to ensure that the flexible cable was UL-listed, so we 
made sure of this when it came from the suppliers. We used 4/0 RHW-2. Now our 
inspector is asking if "RHW-2 is fine-stranded in Article 400 of the NEC as 
required by 690.74?"


Article 400 doesn't explicitly define any cable types for use in battery 
systems, and the one general disclaimer is in 400.4: "Types of flexible cords 
and flexible cables other than those listed in the table shall be the subject 
of special investigation". 


Has anyone had a similar request before? Anyone done a "special investigation" 
on cables, and have results to share? Any other thoughts?


Thanks for any help,


-Phil