Peter, Are you making your measurement before and after the inverter breaker? I believe what you are attributing to the breaker is actually the voltage rise from the service transformer, through the service conductors, through the service panel. A 3-Volt drop is common when adding a 4kW load to a distribution transformer.
Actually, without knowing the load on the transformer to start with, you have several variables. What is likely happening is that the transformer is providing power to the grid on a sunny day before turning off the inverter at say, 2kW. Turn off the inverter, now you instantly turn the inverter from 2kW sourcing to the grid to a 2kW load. The voltage drop, just on the transformer can be a volt or two in the direction of power flow (transformer losses). Let me know if you took the service transformer out of the equation. Bill. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Peter Parrish Sent: Friday, December 10, 2010 9:07 AM To: 'RE-wrenches' Subject: [RE-wrenches] Driving Point Impedance of the Point of Connection of a Grid-tied PV System I wanted to share with the Wrenches a post-install measurement that we make and file along with the other routine measurements (e.g. V(+) to V(-), V(+) to Gnd, V(-) to Gnd, Pac, time or date, date, ambient temp, etc). This is the AC voltage at the distribution panel with and without the inverter operating. For example, let's say we have a 5.5 kW PV system. A clear day in late Fall around Noon might result in 4 kW-ac. We measure the voltage at the distribution panel with both system(s) operating and then throw the AC disco and re-measure. We typically see something around 3 Vac difference. Among other things this measurement provides evidence that a grid tied inverter raises its output voltage/current to the point needed to inject its AC power through the back-fed circuit breaker onto the panel (and from there into the house loads and possibly the grid). One can calculate the "effective resistance" at the backfed breaker, using the formula: R=(2*Vac*dV/dP), where Vac~240V, dV~3V and dP~4000W. In this example the result is 0.36 ohms. And this is close to what we see for relatively new 200A 120/250 split phase panel. >From our way of thinking, this number represents the impedance seen at the back-fed solar breaker which is in turn a function of the resistance of the breaker, the contact resistance of the breaker-buss connection, the resistance of the panel distribution buss, the total resistance of the house loads and the utility feed. The lower this number is the better. We have seen as much as 1.2 ohms in an old 100A Zinsco panel, and this causes us concern. Is anyone aware of an article which discusses the effective circuit model of a back-fed, grid-tied PV system? Or the inferences that one can make from this measurement? What is the normal range of this impedance; or any other similar measurements (such as taking these measurements at the L1-L2 terminal bock of the inverter proper which would include the voltage drop for the inverter-panel circuit)? - Peter Peter T. Parrish, Ph.D., President California Solar Engineering, Inc. 820 Cynthia Ave., Los Angeles, CA 90065 CA Lic. 854779, NABCEP Cert. 031806-26 [email protected] Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885 _______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org _______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org