Interesting in that our AHJ are not up to speed on this. Sealed is sealed to 
them and now I know too.

 

Thanks

 

Dana Orzel

Great Solar Works, Inc

E - [email protected]

V - 970.626.5253

F - 970.626.4140

C - 970.209.4076

web - www.solarwork.com

 

"Responsible Technologies for Responsible People since 1988"

Do not ever belive anything, but seriously trust through action.

 

From: [email protected] 
[mailto:[email protected]] On Behalf Of Exeltech
Sent: Tuesday, December 14, 2010 5:54 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] To insulate a battery bank DEPENDS on a lot of 
factors.

 


If sealed batteries are inadvertently overcharged, H2 and O may be created at a 
rate beyond which the two gasses can be recombined within the cells.  In this 
case, internal seals may open to prevent excessive pressure from accumulating 
and turning the battery into an explosion hazard.  Venting of the enclosure is 
needed for the same reason.  Though sealed batteries are less likely to require 
venting - it's a necessary safety precaution.

Dan


--- On Mon, 12/13/10, jay peltz <[email protected]> wrote:


From: jay peltz <[email protected]>
Subject: Re: [RE-wrenches] To insulate a battery bank DEPENDS on a lot of 
factors.
To: "RE-wrenches" <[email protected]>
Date: Monday, December 13, 2010, 6:30 PM

Hi Dana,

 

The manufacturers that I've read, do say they should be in a vented enclosure.

But your point is taken,

 

thanks,

 

jay

 

 

On Dec 13, 2010, at 8:32 AM, Dana wrote:





Sealed batteries do not require a vent , therefore no air passage – less 
influence of ambient exterior temps to the bank. Perhaps on a small bank this 
would have an influence.

On a large bank in a low usage scenario, IE: second home with no one home, the 
system may be full by 10AM and the fan runs for most of the day inducing cool 
air.

 

Granted most systems have a present [physically] home owner. I have many 
systems that float for a good part of the winter, awaiting the arrival of 
either the owner for a week or spring.

 

Dana Orzel

Great Solar Works, Inc

E - [email protected]

V - 970.626.5253

F - 970.626.4140

C - 970.209.4076

web - www.solarwork.com

 

"Responsible Technologies for Responsible People since 1988"

Do not ever belive anything, but seriously trust through action.

 

From: [email protected] 
[mailto:[email protected]] On Behalf Of jay peltz
Sent: Sunday, December 12, 2010 4:49 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] To insulate a battery bank DEPENDS on a lot of 
factors.

 

HI Dana,

 

I'm curious about why you differentiate sealed vs. flooded batteries?

 

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

 


-----Inline Attachment Follows-----

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

 

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to