Good questions Mark. i've seen distribution feeder voltages adjusted at the substation, as a result of customer complaints, in rare cases. It is fairly common, however, for utilities to make seasonal adjustments at the substation level.
The more common method is to respond to customer inquiry/complaints, of high or low voltage, by measuring & monitoring voltage at the service. If the voltage is found to be out of tolerance one way or the other, they either use different taps on the transformer or replace the transformer to bring it into range. Now you're in the light. -matt -----Original Message----- From: Mark Frye Sent: Monday, December 20, 2010 9:06 AM To: 'RE-wrenches' Subject: Re: [RE-wrenches] Low grid voltage fix How do utilites go about adjusting the voltage at any given site? Adjustable taps on the transformers on the poles? Do they have to go back to the nearest sub-station? Re-arrange the distrubution of customers across differenat areas of the grid. _______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org