Drake Let me explain, I have worked with the large inverter 4kW and Magnum 4024 AE extensivly, trying to get it right. The Magnum was starting a large motor reliably (in fact it never missed), but the Outback did not start the motor at all well. So I settled on the Magnum, and did little work on this install with the Outback.
Yes the Outback and the Magnum caused the DGI inverter to drop out, but I was not understanding what was happening, and I am not sure I got it correct. But with the magnum I was trying to make it work with a 4 kW DGI inverter and it would work fine as long as the solar was not to bright or all the panels were hooked up. I went through several tests with the Magnum (days)and every time it got over 50% the posibility of shutdown. I tried over and over again. I did not do this with the Outback as it turned out, but I have had unexplained bright sun cold modules when near 50% load DGI kickout, with the Outback. I would like to know if the Magnum 4024 PAE would be the same and if two magnums would handle the load, but we are all limited finacially. --- On Mon, 12/27/10, Drake <[email protected]> wrote: > From: Drake <[email protected]> > Subject: Re: [RE-wrenches] Component Choices for MY RV - Apollo Solar? > To: "RE-wrenches" <[email protected]> > Date: Monday, December 27, 2010, 9:10 AM > Have you found the 50% capacity true > for Outbacks? I'm considering > AC coupling 2000 watts into a VFX 3524. With the roof > angle, on cold > days, this inverter could get STC solar production easily. > > Drake > > > At 07:53 PM 12/25/2010, you wrote: > >I have answered an eariler email, but in regards to > backfeed, I have > >back feed up to 2kW of grid tied inverter into my > Magnum 4024 AE and > >it held grid specification for the DGI inverter. > Above 2kW into the > >Magnum the Grid tied inverter kicks out on frequency > >specification. Other inverters do the same for > me, cause DGI kick > >out also at about the same level ie about 50% of > capacity. Sorry I > >do not have many examples of this. but I do not have > any contra > >indictating examples. > > > >--- On Thu, 12/23/10, bob ellison <[email protected]> > wrote: > > > > > From: bob ellison <[email protected]> > > > Subject: Re: [RE-wrenches] Component Choices for > MY RV - Apollo Solar? > > > To: "'RE-wrenches'" <[email protected]> > > > Date: Thursday, December 23, 2010, 6:58 PM > > > There are a couple things on the > > > Magnum inverters that you will learn about > > > after using one that really need to be > corrected. > > > DO NOT backfeed them, they are not protected like > most > > > other inverters. Back > > > feed them and BAD THINGS WILL HAPPEN! Read that > as > > > expensive. > > > > > > Also the split phase 120/240 inverters are slow > to recover > > > from a voltage > > > drop. I have never noticed this on the 120 volt > units but I > > > don't have any > > > large loads anymore so I would not see it like > someone with > > > a well pump or > > > other large surge loads. I have had several calls > about > > > this from customers > > > and it is real. If this is a problem or not seems > to depend > > > on the customers > > > attitude, but it can be annoying. > > > > > > At least they are still made here, and the > service is > > > good! > > > > > > Bob Ellison > > > > > > > > > > > > > > > -----Original Message----- > > > From: [email protected] > > > [mailto:[email protected]] > > > On Behalf Of Brian Faley > > > Sent: Thursday, July 01, 2010 2:20 PM > > > To: [email protected] > > > Subject: [RE-wrenches] Component Choices for MY > RV - Apollo > > > Solar? > > > > > > > > > > > > Hi Jeff, > > > > > > Just a couple comments to answer your question > about Magnum > > > inverters. > > > See below. > > > > > > > > Message: 6 > > > > Date: Thu, 1 Jul 2010 06:09:35 -0700 > > > > From: Jeff Clearwater <[email protected]> > > > > To: RE-wrenches <[email protected]> > > > > Subject: [RE-wrenches] Component Choices for > MY RV - > > > Apollo Solar? > > > > Message-ID: > > > <p06240800c8523ddca...@[74.220.67.154]> > > > > Content-Type: text/plain; > charset="iso-8859-1" ; > > > format="flowed" > > > > > > > > Dear Colleagues, > > > > > > > > Well this one's for me! Nice to do > solar for > > > > oneself after installing for others my whole > life! > > > > > > > > I'm putting together an small RV system in > my > > > > Sprinter Van that will also act as a small > mobile > > > > power platform. SUGGESTIONS? > > > > > > > > I'm considering the > following: What > > > would be better??? > > > > > > > > Batteries: 6 or 8 Optima Blue Tops (12 > Volt > > > > System - possibly 24V) (space is limited - > it's a > > > > 144" Sprinter Van) - Other sealed > alternatives > > > > you think are better? > > > > > > > > Modules: 2 Sanyo HIP-195BA19s (have > > > already) & > > > > 1 undetermined 90-120 watt module (all that > will > > > > fit!) (Anyone have an extra BP 790 or > an > > > > AE-90HE, AE-120HE??? or other 24" x 48" ish > > > > module?) > > > > > > > > Charge Control: OB FlexMax 60 or > should I > > > wait > > > > for the Midnight Classic? (A Sunsaver > MPPT will > > > > be used for the 100 watt module). > (I'll also be > > > > dumping extra power to hot water). Or > Apollo if > > > > I use the Apollo inverter below. > > > > > > > > Inverter: I'd like to eventually have > 120/240 > > > so > > > > I could build from the RV. So question > is: > > > > > > > > A) One Outback 2012 now and then add another > for 240 > > > VAC later OR > > > > B) Apollo TSE2212 OR > > > > C) Magnum MS 4024 (in which case I'd have to > go > > > > with a 24V pack and a 24>12 DC>DC for > 12V > > > loads) > > > > > > The Magnum MS4024 is a 120V inverter for AE and > mobile > > > applications. The > > > MS4024AE is a 120/240 split phase inverter for > AE > > > applications. > > > > > > > > Monitoring: OB Mate (Flexnet?) or > (Apollo ASNET > > > if I go Apollo). > > > > > > > > QUESTIONS? > > > > > > > > 1) Opinions of the Blue Top > vs ??? > > > > > > > > 2) Best RV inverter - Outback? > > > Apollo? Magnum? > > > > Experience? Vibration? Only the > Outback > > > offers > > > > neutral switching in the transfer switch. > (Does > > > > the Magnum?). > > > > > > Magnum MS4024 (120V single phase output) has > neutral/gnd > > > switching in > > > the transfer switch of the inverter. It is ETL > listed to > > > UL458 (mobile > > > inverters) AND UL1741. > > > The MS4024AE is a 120/240 split phase inverter > intended for > > > AE use > > > (non-ground switched) It is ETL listed to > UL1741. > > > > > > Weight is an issue as well as > > > > space. > > > > > > MS4024 4kW inverter 55lbs > > > > > > > > 3) Charge Control - Is the Classic > Shipping? > > > > > > > > Thanks for your time! > > > > > > > > Best, > > > > > > > > Jeff C. > > > > > > > > -- > > > > ~~~~~~~~~~~~~~~~~~~ > > > > Jeff Clearwater > > > > Village Power Design > > > > > > > > Solar Design Consultation for the Commercial > Sector > > > > http://www.villagepower.com > > > > [email protected] > > > > > > > > NABCEP Certified Solar PV Installer ? > > > > http://www.nabcep.org/ > > > > > > > > Voice: 831-427-2799 > > > > Fax: 413-825-0703 > > > > 245 Dufour St > > > > Santa Cruz, CA 95060 > > > > ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ > > > > > > Regards, > > > Brian Faley > > > Chief Engineer > > > Magnum Energy, Inc > > > 2211 West Casino Rd, Everett, WA 98204 > > > 425-353-8833 voice > > > [email protected] > > > www.magnumenergy.com > > > > > > > > > _______________________________________________ > > > List sponsored by Home Power magazine > > > > > > List Address: [email protected] > > > > > > Options & settings: > > > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > > > > > List-Archive: > > > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > > > > > List rules & etiquette: > > > www.re-wrenches.org/etiquette.htm > > > > > > Check out participant bios: > > > www.members.re-wrenches.org > > > > > > _______________________________________________ > > > List sponsored by Home Power magazine > > > > > > List Address: [email protected] > > > > > > Options & settings: > > > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > > > > > List-Archive: > > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > > > > > List rules & etiquette: > > > www.re-wrenches.org/etiquette.htm > > > > > > Check out participant bios: > > > www.members.re-wrenches.org > > > > > > > > > > > > > >_______________________________________________ > >List sponsored by Home Power magazine > > > >List Address: [email protected] > > > >Options & settings: > >http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > > >List-Archive: > >http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > > >List rules & etiquette: > >www.re-wrenches.org/etiquette.htm > > > >Check out participant bios: > >www.members.re-wrenches.org > > _______________________________________________ > List sponsored by Home Power magazine > > List Address: [email protected] > > Options & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out participant bios: > www.members.re-wrenches.org > > _______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org