I had a similar situation in Minnesota, my local inspector was puzzeled but the regional inspector said ABSOLUTLY the solar equipment has to be shut off with no more than 6 motions of the hand. I combined the AC into a panel of 12 breakers, with one main (i had 12 inverters). For the DC side I did something DT but I could have used 2 each 6 pole Square D 600 volt 30 amp Disconnects or 3 each 4 pole, or 4 each 3 pole to complete the disconnect requirement Darryl
________________________________ From: Al Frishman <[email protected]> To: [email protected] Sent: Wed, January 12, 2011 3:11:17 PM Subject: [RE-wrenches] 690.14 (4) Max Number of Disconnects Hi Wrencher’s I am working on a system with 10 inverters. The output of all 10 single phase inverters will be combined in a main lug only panel located on the 8th floor (each inverter will have a 2 pole breaker). The MLO Panel will be protected by a fused switch located in the basement. Does the panel on the 8th floor used to combine all 10 inverters need to have a main breaker in order to comply with 690.14 (4)? Any and all feedback is appreciated. Al Frishman AeonSolar (917) 699-6641 - cell (888) 460-2867 www.aeonsolar.com
_______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org