"Warning: those old DIY setups quickly become a can of worms, the
further you dig into them. Don't assume anything was done right."
...Including checking the polarity of every wire! Who knows what the
color meant to the last guy.
And don't just mess with a few things and leave it. That customer is
sure to have more problems and you were the last to touch it. (God
forbid if they have an electrical fire.) Tell them it will take time
to fix the mess. Make yourself a wiring diagram following every
wire. This will take some customer investment, but result in a
working system and happy customer.
Blessings,
Kelly
Kelly Larson
Box 104
Piercy, CA 95587
707-223-3209
Electrical Engineer
NABCEP Certified Solar PV Installer
ISPQ Master Trainer
CA C-10 # 868189
[email protected]
"I'd put my money on the sun and solar energy. What a source of
power! I hope we don't have to wait until oil and coal run out before
we tackle that." ~ Thomas Edison
On Dec 29, 2010, at 10:59 AM, R Ray Walters wrote:
Jay;
I've saved a few sets from freezing, different manufacturers' cases
are stronger than others. (ie, A Trojan T105 can take more stress
than something from Sam's Club.)
FIrst I make sure they're less than 5 years old.
Then, I warm them backup (portable propane heater, very well vented
area, no current flow in or out)
3rd, See if any are leaking
4th, Charge them with the caps off, monitoring voltage, current,
temperature, and bubbling action.
Jesse;
Your eyes and health are not worth risking to save those old things;
12 years is a fairly respectable lifespan in a poorly setup system.
I think to continue to work with those batteries is inviting danger
(everyone's recent explosion stories?)
All those problems were caused by shorting plates, and other
malfunctions, usually only seen in old batteries.
Batteries only freeze when completely abused. The inverter probably
was shutting off all the time from low voltage, and they had DC
loads dragging it down even lower.
The recent string on battery temperature management should be
applied in this case too. I've seen poorly designed venting, freeze
batteries right next to it, while the batteries on the inside
were warm.
I agree with Allan's assessment: this set is toast, and considering
this is the worst time of year to not have a good battery set, I'd
take care of that lady, and get her into a fresh set, ASAP.
This is also a chance to do some needed rewiring of the system.
Warning: those old DIY setups quickly become a can of worms, the
further you dig into them. Don't assume anything was done right.
R. Walters
[email protected]
Solar Engineer
On Dec 29, 2010, at 9:16 AM, jay peltz wrote:
I'd like to go back to the freezing battery part as I don't live in
real freezing territory.
How could they actually freeze and not destroy the housing,
internal plate structure and in the end work at all?
thanks,
jay
From: [email protected] [mailto:[email protected]
] On Behalf Of Allan Sindelar
Sent: Wednesday, December 29, 2010 10:41 AM
To: [email protected]; RE-wrenches
Subject: Re: [RE-wrenches] Trace inverters undercharging batteries.
Jesse,
Don't waste your time on those batteries; they are all toast.
Don't replace them with the same; four strings is poor design.
Read the article about off-grid batteries in the current Home
Power, and then sell the customer a set of 12 (or 24; either one
string or two is OK) 2V industrial cells, such as HUPs from
Northwest Energy Storage or K-series Surrettes. Size unknown. The
existing full bank was 1400 A/hr if the cell cases had black
covers, 1600 A/hr if the tops are blue, to give you an idea.
BP modules from 1998 would have most likely been 12V 75W or 85W,
meaning 900-1000 watts; too small an array for that size battery
bank if the home is used full-time; OK for a seasonal or weekend
cabin.
Only with new batteries can you even tell what the inverters are
doing. My hunch is that the inverters aren't at fault. However,
given the poor quality of the original installation, they likely
are set to default setpoints, which can charge at a very high rate
(about 220A at 28.8V for two if the gennie is big enough) but
won't get batteries full (and can't equalize them), as the default
setpoints are too low. And I'll bet dollars to doughnuts the
default setpoints are in place, as the inverters have been shut
down sometime in the last 12 years, losing any original
programming settings.
You might see about getting an experienced off-gridder in your
frozen region to work with you. Maybe Darryl could consult now,
then make one trip out to set up the system once the new batteries
are in. This was the classic late-90s system with a later charge
controller upgrade, but if you have never worked with this
equipment, you're likely to set it up for a repeat failure years
down the road.
Just read Jamie's post - while his advice is spot on, of course,
you need to decide if it's worth your while. I'd be more inclined
to try his approach if the battery bank was three years old, not
12. That's a huge amount of time spent, working with acid and an
unknown set of hazards, with at best the possibility of a few
years' use. I'd suggest that unless it's your father-in-law's
cabin, and you value the chance to hang out there for a week, it's
not worth your time or the customer's, especially given that you
acknowledge having little off-grid experience.
Allan
Allan Sindelar
[email protected]
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org