August,
If the SI does, indeed, shut out the pass-through AC channel when the critical load panel is connected directly to the grid this is certainly a simpler solution. That would explain why the GD inverters would drop out during a switch. Is the switch-over is fast enough that time-keeping gizmos will not have to be reset? Ours is an on-grid customer, with on-grid expectations.

We'll confirm that this connection is approved by SMA.

Thanks, again.
-Kelly

Kelly Keilwitz, P.E.
Whidbey Sun & Wind
Renewable Energy Systems
[email protected]
360-678-7131




On Jan 14, 2011, at 10:07 AM, August Goers wrote:

Hi Kelly -

Yes, AC1 from the Sunny Island is always connected to the critical loads
panel. During on-grid operation the critical loads panel is fed solely
through the main panel and transfer switch, not through the Sunny Island.
I see your question about paralleling the critical loads panel through
both the external transfer switch and the Sunny Island. It's been a while since I've contacted SMA about this but my understanding is that the Sunny
Island is "smart" and since it sees that there is already power on the
critical loads panel it will not backfeed the critical panel until it sees
that the main power goes down.

When the grid power goes down the automatic transfer switch flips very
quickly to backup mode and the Sunny Island immediately kicks in. It
happens so fast that the first few times I was testing it I was caught off
guard and thought that something was wrong. In fact it was flipping to
backup mode so fast that I didn't even see the lights flicker. Even though this switch is really quick the grid tied inverters still trip off in my
experience.

Does this address your thoughts?

Best,

August



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Kelly
Keilwitz, Whidbey Sun & Wind
Sent: Friday, January 14, 2011 9:35 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] AC coupled, grid-tied Sunny Island - contactor
& bypass

Hi August,
To make sure I'm clear:
Does the Sunny Island output (AC1) stay connected to the critical load
panel while at the same time fed directly from the main panel?

If so, is there no issue with the critical loads being fed through
multiple paths? And, why, then, would the GD inverters switch off
during the switch if they continue to have an AC signal from the SI's.

If not, you must be switching the critical load panel feed between the
SI AC1 and main, via the transfer switch. And, the drawback would be
that the critical loads would not have an uninterruptible power supply
during a grid outage.

Thanks for your description. This certainly sounds simpler than my plan.

-Kelly

Kelly Keilwitz, P.E.
Whidbey Sun & Wind
Renewable Energy Systems
[email protected]
360-678-7131




On Jan 14, 2011, at 7:23 AM, August Goers wrote:

Hi Kelly -

Sounds like a fun project. We've got a few 10+ kW grid tied Sunny
Island
projects and although they are not with Enphase inverters I thought
I'd
pass on how we've been wiring them up with good results.

We tie the solar inverters into the critical loads panel and then
put a
transfer switch (either auto or manual depending on the client's
choice)
between the main and critical loads panel. The Sunny Island(s) output
circuit (AC1) is also tied into the critical loads panel and the AC2
connection is tied into the main. During normal on-grid operation
the PV
is tied directly to the main through the critical loads panel and
transfer
switch so there are no losses through the Sunny Island. The Sunny
Island
at that point is simply keeping the batteries charged though the AC2
connection and monitoring the grid. When the grid goes down the
transfer
switch disconnects the critical loads panel from the main and the
Sunny
Island kicks in. The PV inverters shut off immediately during the
switch
but then kick into waiting mode once receiving the signal from the
Sunny
Island. The PV stays on during the grid outage until the batteries are
fully charged then the voltage increases until the PV turns off,
goes back
into waiting mode and the whole process repeats - this is assuming
that
we're getting more PV than load. I've tested both scenarios and if the
load is larger than the PV then the inverters will stay on
indefinitely.


What was your reasoning for tying the PV into the main and using a
relay
to switch to the critical loads panel during a power outage?

Best,

August


August Goers

Luminalt Energy Corporation
1320 Potrero Avenue
San Francisco, CA 94110
m: 415.559.1525
o: 415.641.4000
[email protected]

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Kelly
Keilwitz, Whidbey Sun & Wind
Sent: Thursday, January 13, 2011 7:33 PM
To: RE Wrenches listserve
Subject: [RE-wrenches] AC coupled, grid-tied Sunny Island -
contactor &
bypass

Wrenches,
We are including 2 Sunny Island inverters into a previously battery-
less grid tied design utilizing 20 kW of PV on Enphase micro inverters
and 2 SMA Windy Boy 6000 inverters (10 kW XZERES 442 turbine). Our
customer wishes to run his fuel generator as little as possible when
the grid goes down. Nothing is in the power room yet, the house is
under construction. Only the wind turbine is installed.

With a pass-through limit of 56A, the two Sunny Islands cannot conduct
the combined RE production to the grid. There is not enough critical
load demand to justify two more SI's, nor is there space for them. Our
plan is to connect the micro-inverters (84A, peak) directly to the
main service (grid) in normal mode, switching to the critical load
panel (SI AC output) when the grid goes down. The Windy Boys (56A)
would remain connected to the critical load panel.

I'm hoping that the frequency shifting control of the Windy Boys from
the SI's will allow the PV micro inverters to connect and stay
connected to the SI's while there is demand on the critical loads and
the batteries are charging. When there is more PV output than load
demand we expect that the SI frequency will rise to the point where
the micros will go out of spec and disconnect, maybe in a nicely
staggered pattern.

Questions:

1. Has anyone experience with this much grid-direct RE capacity and/ or
micro-inverters AC coupled to Sunny Islands? I'm a little scared by a
previous post from Darryl wherein he found that the RE capacity from
the GD inverters should be 1/2 that of the battery-based inverters in
an AC coupled system. Please let me know if you are certain that this
is not going to work!

2. Any experience with specifying a contactor/relay to switch the PV
output? The contactor will be controlled by one of the SI relays.
Switching from the main panel (grid) to the critical load panel will
be during a grid outage, so doesn't need to be load-rated, but
switching back after the grid comes back up could be load-break. Our
current solution is to use two 80A contactors from Schneider
(#LC1D80G7) with an intertie kit.

3. Any suggestions for an inverter bypass (service disconnect) for the
two SI's? We're considering either a monster 2P2T 200A switch (100 A
would do), or using a gen-transfer type panel for the critical loads.

Comments and informed opinions quite welcome.

Thanks,
-Kelly

Kelly Keilwitz, P.E.
Principal
Whidbey Sun & Wind
Renewable Energy Systems
[email protected]
PH & FAX: 360.678.7131
NABCEP Certified PV Installer
WA Electrical Administrator







_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to