It seems as though almost every utility has a different requirement concerning 
Utility External Disconnects and the AC disconnects for the PV system in 
general.  Some utilities require lockable blade style disconnects while others 
will accept the backed breaker in a load panel(if outside) as the photovoltaic 
AC system disconnect.  My question refers to situations where grid tied 
inverters and the AC point of connection are both inside a dwelling.  
Specifically, if a grid tied inverter is located inside a garage and it's 
output is connected to a back fed breaker in the main panel (also in the 
garage), can the utility disconnect at the meter serve as both the utility and 
PV system AC disconnect?  I see nothing in the NEC that says the PV system's 
external AC disconnect has to be independent of the utilities' disconnect.  Can 
this one breaker act as the disconnect for two sources of power? Any thoughts 
would be appreciated.  

Aaron Mandelkorn
Renewable Energy Outfitters
P.O. Box 65 
Salida CO 81201
(970)596-3744
reoso...@gmail.com
www.reosolar.com