Mark,
As you know it depends on two things. What the grid voltage is and at what 
voltage the Enphase inverters stop pushing current (check with enphase, it 
could actually shut down at lower than 264vac). The grid voltage is the unknown 
here. If it is 245vac adding a 4% line loss results in 254.8vac at the 
inverter. If 254vac grid then 264 at the inverters with a 4% loss. 
We had case where a Sunny Boy was shutting down because of high grid voltage. 
The utility adjusted their voltage down at the transformer taps. They knew that 
voltage was high in this neighborhood (256vac), they said that they had been 
meaning to correct that problem soon anyway. They brought it down to 246vac and 
no more problems for the SB inverter.
Dave  
Sent via BlackBerry by AT&T

-----Original Message-----
From: "Mark Frye" <[email protected]>
Sender: [email protected]: Mon, 14 Feb 2011 
19:42:11 
To: 'RE-wrenches'<[email protected]>
Reply-To: RE-wrenches <[email protected]>
Subject: [RE-wrenches] Can I handle the voltage drop?

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to