I'd like to suggest that Appendix J of John Wiles Suggested Practices Photovoltaic Power Systems and the NEC be read. It provides good instruction on how to calculate when an OCPD is needed. It is a function of the module's Isc rating, the inverter's backfeed current capabilty, and the module's maximum series sting fuse rating. The rule of thumb is fusing is usually required above two paralleled sub array circuits, but with some modules, a greater paralleled number of subarrays can be installed without fusing. It does make troubleshooting more difficult and as said, it is inexpensive to spec subarray fusing.
Chris

On 2/21/2011 3:51 PM, Phil Schneider wrote:
Dan,

My understanding has been that unless the inverter spec lists a "0 A backfeed current" then it is conceivable that fault current from the grid (up to the inverter OCPD) could feed a fault on the DC side, so DC fusing would be necessary (Fronius IG Plus spec sheet, for example, states this). SMA specs state the maximum backfeed current to be equal to the maximum OCPD for a given inverter size. However, I've asked SMA tech support about this directly, and they assured me that it isn't possible for current from the AC side to reach a fault on the DC side. This is not very clear to me, but the cost of fusing two strings is generally quite low, so when I doubt I spec fusing. Curious to hear if others think this is too conservative.

P.

Phil Schneider
Creative Energies
p 307.332.3410
c 307.438.1195
f 888.456.6625
www.CreativeEnergies.biz <http://www.CreativeEnergies.biz>



On Mon, Feb 21, 2011 at 12:52 PM, <[email protected] <mailto:[email protected]>> wrote:

    Hey Everybody.. I got the impression that 690.9 ex. allows up to
    two parallel strings to be connected (thru a disconnect) to a grid
    interactive inverter (which does provide Ground Fault
    Protection).. Do I still need to protect the Array from possible
    inverter back feed? This particular array consists of two pole
    mounted arrays out in the boonies in the middle of a field. The
    Inverter is mounted on one of the poles...  Let the egg toss
    begin... db


    Dan Brown
    Foxfire Energy Corp.
    Renewable Energy Systems
    (802)-483-2564
    www.Foxfire-Energy.com <http://www.Foxfire-Energy.com>
    NABCEP #092907-44

    _______________________________________________
    List sponsored by Home Power magazine

    List Address: [email protected]
    <mailto:[email protected]>

    Options & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>




_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options&  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules&  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


--

Christopher Warfel, P.E.
ENTECH Engineering, Inc.
Energy Utilization Experts
(401)466-8978

The information contained within this communication shall
be considered confidential and shall not be retransmitted
without knowledge of the sender. Please contact us if
this email reached you in error. Thank you.

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to