Allan,

I used Quick Cote for years until my local supplier had problems getting it in a timely manner.
I never had a problem with it but then again, I never put it on the lug/ terminal mating surfaces
prior to making the connections. Then I carefully coated the terminals, making sure to not
miss any spots.

I've had several opportunities to have a look at the mating surfaces years later and never found
any corrosion. I would imagine that grit would indeed create a connection problem. But you say
you've never seen this yourself?

I wonder if the formulation has been changed recently?
Roy Butler
NABCEP Certified Solar PV Installer®
NYSERDA eligible PV & wind installer
PA Sunshine Program Approved PV Installer
Four Winds Renewable Energy, LLC
8902 Route 46
Arkport, NY 14807
607-324-9747

www.four-winds-energy.com

Although no trees were killed in the sending of this message, 
a large number of electrons were terribly inconvenienced.

                

On 2/22/2011 7:12 PM, Allan Sindelar wrote:
Wrenches,
Russ in our Taos office sent me the following query. I haven't seen this problem before and told him so, but others among you may know more.

What problems if any have you had with Quick-Cote battery terminal coating? What else works really well and lasts the life of the batteries?

From Russ:
We just had a situation involving Quick Cote on battery terminals that has made us question its use for coating battery terminals and cable lugs.  We just installed a bank of HUPs on Monday using Quick Cote.  First we lost power with just the Trimetric and MX60 powered up -- using an ohmmeter I found the problem to be a single jumper -- I got 7 megohms across two battery terminals connected by a jumper -- so I replaced the jumper and got the Trimet and MX60 powered up again.  Then, when I powered up the OutBack inverters, there were sparks on the battery terminals, and the power cut out again.  At that point I guessed that the problem must lie with the Quick Cote, since ours has tiny crystals in it (it feels gritty), and I thought those crystals must be holding the cable lugs off the battery terminals a tiny bit.  Sure enough, Mark and I took the cables off, wiped off the Quick Cote from the contact surfaces and applied vaseline, and when we powered up the system, no sparks.  (So, the jumper I removed probably wasn't to blame for the first loss of power.)

Our container of Quick Cote stayed on the truck (which stays parked outside) during the seriously cold weather we got this winter, so it probably froze.  I'm guessing that's when the crystals formed.  Nowhere on the Quick Cote label does it say to keep it from freezing though.

We're going to go back out to another job to wipe off the Quick Cote from the contact surfaces of the battery terminals and cable lugs, since we just installed four new batteries there and used Quick Cote, and I remember it being gritty at that time as well.

Is your Quick Cote gritty?

Russ


I told Russ that it always has been gritty. When it's dried out in the can (they often leak), I have added an oil-based carrier to thin it - usually WD40, as it's on the truck - and it's always mixed easily. So it's definitely solvent-based and shouldn't be affected by freezing.

I haven't had this problem before. I have found terminal bolts too loose and that has caused failures, but never the coating.

Thank you,
Allan

Allan Sindelar
Allan@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com


_______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to