Ray,
   I solved the problem of the small inverter/generators kicking out by just 
making the generator and an IOTA charger as a subsystem..  I find the best 
charger match for the small generator and hook up to the batteries.  I started 
doing this with grid tie with backup systems as the GVFX inverters can't handle 
a generator input.  It worked well for the grid tie setups so I recommend it to 
anyone off-grid looking for fuel efficiency but also having to start well pumps 
etc.   I recently put in a Wrico diesel generator at my house, replacing a 
Honda 2000i and sure do miss the fuel efficiency.



-----Original Message-----
From: R Ray Walters <[email protected]>
To: RE-wrenches <[email protected]>
Sent: Wed, Mar 16, 2011 4:46 pm
Subject: Re: [RE-wrenches] Generators?


Hi Daryl;


DId you AC couple it to the Outback AC output? or did you use the AC in on the 
Outback?
I liked the little 1 Kw Yamahas for battery charging, but they are so small 
that if any loads come on in the house, the pass through loads will trip the 
Yamaha's overload circuit, and quit charging.
Worse, the genie keeps running even though its not producing any power, so the 
customer has no idea its not charging and can run the genie for hours in this 
useless mode.
We moved away from the tiny gennies because of this problem. Even when working 
they were not even equal to the array in full sun.
In my opinion, you need to size the genie to provide a full day's energy needs 
in about 4 hours of battery charging. (thus 3 days without sunshine would 
require 12 hours of generator run time)
This roughly translates to a genie that is at least double the power rating of 
the array. I like the genie to be quadruple the array power  these days, or an 
8Kw gen set for a 2Kw array.
Totally depends on the weather and location, as well. (and don't forget the 
derating for altitude)


R. Walters
[email protected]
Solar Engineer








On Mar 16, 2011, at 12:22 PM, Darryl Thayer wrote:



a little off topic but I just connected a 1 kW generator (yamaha inverter) to a 
2 kW solar and a Outback FX 3524 and a PVPowered 1100 with 1 kW AC coupled, it 
just plain worked.   no problems.  I do not know how well the other inverter 
generators work, but this is a case where when the batterys get low in this off 
grid vacation home, they can easily be recharged with solar and gen set.
DT 



From: Nathan Jones <[email protected]>
To: [email protected]
Sent: Wed, March 16, 2011 12:23:24 PM
Subject: Re: [RE-wrenches] Generators?

August,
Most of the units around 8kw are lower quality units. Most are going to be 3600 
rpm instead of 1800 rpm. I just saw an excellent writeup on gensets in a back 
issue of Home Power written by Alan Sindilar??? Sorry about the spelling,  
Alan. Excellent article. Perhaps someone knows the issue date.
Nathan Jones

On Wed Mar 16th, 2011 11:58 AM CDT August Goers wrote:

>Hi Off Grid Wrenches -
>
>I need to select a propane generator to provide a steady state load of
>approximately 8 kW for a offgrid Sunny Island system. The project is for
>an art studio and the loads are primarily all lights.
>
>I don't have much experience with generators so I thought I'd reach out
>and see what products and manufacturers are popular out there.
>
>Thanks,
>
>August
>
>
>August Goers
>
>Luminalt Energy Corporation
>1320 Potrero Avenue
>San Francisco, CA 94110
>m: 415.559.1525
>o: 415.641.4000
>[email protected]
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: [email protected]
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
>



      
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





= 

_______________________________________________
ist sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
ttp://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
ww.re-wrenches.org/etiquette.htm
Check out participant bios:
ww.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to