Larry and Kent

We did an XW system several months ago, feeding a dedicated loads panel of 
course. The owner wanted to fill out the roof space so we added 9 modules w/ 
190 W Enphase connected to the main panel. My understanding is that when the 
grid goes down, the Enphase goes off line, and the XW transfer switch also 
isolates from the grid. The XW powers the dedicated loads panel from the 
batteries/PV array. 
Later , the owner purchased a generator and plugged into the receptacle we had 
provided, wired to the AC2 ( GEN )input to the XW. The generator can charge the 
batteries, and support the XW output for heavy loads. There is no connection to 
the main panel, nor the Enphase inverters.
When the grid comes back online, both the XW and the Enphase take several 
minutes to sync to the grid, and then the XW disconnects from  the Gen. input 
and powers the dedicated loads, sells back to the grid if the PV is producing 
more than the dedicated loads are drawing, or allows the grid to 'pass thru ', 
thus not depleting the batteries.
After the owner purchased the generator , we tested operation by disconnecting 
the AC1 breaker, verifying the Enphase shutdown, turning on many loads in the 
dedicated loads panel, and  starting the generator to recharge the batteries. 
Everything works perfectly. 
By the way, we have had no problems with the XW equipment--both 4500W and 
6000W. The first XW we did several years ago , when they first became 
available, needed a software upgrade, so we purchased the Configuration tool, 
which is also handy for some monitoring of performance.
Hope this helps------

Ken Schaal
CommonWealth Solar
  ----- Original Message ----- 
  From: Kent Osterberg 
  To: RE-wrenches 
  Sent: Sunday, March 27, 2011 5:13 PM
  Subject: Re: [RE-wrenches] Generator and Enphase


  Larry,

  The XW has separate Grid and Gen inputs. It's designed to sell power to the 
grid and it makes sense that the XW wouldn't sell to the generator. But I don't 
think it can stop a microinverter from trying to sell power to the generator. 
If the generator is on and the transfer switch is closed, what would stop power 
from flowing backwards through the transfer switch?

  Kent Osterberg
  Blue Mountain Solar



  [email protected] wrote: 
    This doesn't solve the reliability concern of a contactor but on a webinar 
I heard a rep from Schneider say the XW (with GEN and GRID AC IN's) will not 
backfeed a generator and will do it without a contactor. Is that true? 


    Larry Liesner
    Wirewiz
    Westport, CT
    Phone: 203-644-2404
    Fax: 203-557-0556
    [email protected]
    www.wire-wiz.com






    On Mar 27, 2011, at 3:50 PM, Kent Osterberg wrote:


      Larry,

      Yes, the PV system was straight grid-tie. The back-upped loads were only 
covered by the generator (no battery-based inverter was involved). The ATS also 
does the generator startup, so an inverter on the backed-upped loads would 
require some thinking I haven't done. If the generator startup were changed, my 
first thought would be to put the battery-based inverter on the generator side 
of the ATS.

      Kent Osterberg
      Blue Mountain Solar 



      [email protected] wrote: 
        Kent,


        Situations vary but this one line helps a lot, thanks.


        So,  "To PV System" would go to the output of a grid tie inverter and 
"To Backed Up Loads" would go to the AC IN (transfer switch) of a battery 
inverter. 


        I have been going to homes with existing 100A gen/utility ATS and 
wondering if I could keep it as is and be able to add a grid tie battery backup 
to it (using same backup loads). This schematic would work in that situation as 
well but wouldn't have the "To Non-Backed UP Loads" tap.




        Larry Liesner
        Wirewiz
        Westport, CT
        Phone: 203-644-2404
        Fax: 203-557-0556
        [email protected]
        www.wire-wiz.com






        On Mar 27, 2011, at 2:36 PM, Kent Osterberg wrote:


          Larry,

          Situations vary so much that this might not be very useful. But here 
you go. The attached sketch shows how we recently connected a customer that had 
a backup generator and transfer switch that wasn't service rated. There were 
nice gutters existing from the original install so accessing points to tap 
conductors wasn't difficult. We could have connected the inverters to the 
non-backed upped loads panel instead, but the utility requires an accessible 
disconnect by the meter so it was more convenient to just get into the gutter.

          Kent Osterberg
          Blue Mountain Solar



          [email protected] wrote: 
            Kent, Jason, or anyone else 


            Would you a have a simple one-line you could share for wiring the 
inverter on the utility side of the transfer switch? 


            Thank you.


            Larry Liesner
            Wirewiz
            Westport, CT
            Phone: 203-644-2404
            Fax: 203-557-0556
            [email protected]
            www.wire-wiz.com






            On Mar 26, 2011, at 6:04 PM, Jason Szumlanski wrote:


              We’ve explored this strategy many times due to all of the whole 
house and critical load generators in Florida. We’ve stayed away from the 
contactor solution because of the potential for the NC contactor failing to 
open, keeping the inverters “online” when transferred to generator power. While 
unlikely, this is a possibility that must be considered.
              The other issue presented here is that the inverters will shut 
down every time the generator exercises.
              The only sure-fire way seems to be wiring the inverter on the 
utility side of the transfer switch, as Kent said.
              Jason Szumlanski
              Fafco Solar
              From: [email protected] 
[mailto:[email protected]] On Behalf Of Kent Osterberg
              Sent: Saturday, March 26, 2011 5:56 PM
              To: RE-wrenches
              Subject: Re: [RE-wrenches] Generator and Enphase
              Mark,

              I agree it is best to wire the inverters on the utility side of 
the transfer switch. When that isn't easy, a normally closed contactor that is 
opened by generator voltage, will isolate the inverters from the generator and 
allow automatic return to utility operation when the generator is off.

              Kent Osterberg
              Blue Mountain Solar



              Mark Frye wrote:
              Eric,
              I do not have direct experience with this but have been exploring 
the issue for a project I am currently doing.
              My response will be to take the trouble to interconnect the 
Enphase inverters on the line side of the tranfer switch so that the inverters 
can never be connected to the generator.
              Here are the reasons why:
              1 - Enphase states that any such application is considered an 
"off-grid" application which voids their warrenty. As I am installing under the 
California CSI program, I am required to provide a 10 year manufacture 
equipment warranty so I cannot afford to install the inverters in a dis-allowed 
manner.
              2 - Enphase states that the waveform of the generator may be 
"clean" enough such that the inverter may attempt to syncornize and connect to 
it as if it were the utility. If this were to happen Enphase believes the 
inverters will ruin the generator regulator before the generator ruin the 
inverter. I don't want to be the one to run the experiment to find out which 
would be which.
              3 - I considered a contactor on the output of the inverters, such 
that the inverters would isolated by a loss of line voltage, requiring some 
form of reset. Ulitmately my customer agreed with me that this was an 
undesirable constraint on the operation of an otherwise reliable grid-tied 
system and it was not clear that this would satify the warranty issue.

              Mark Frye 
              Berkeley Solar Electric Systems 
              303 Redbud Way 
              Nevada City,  CA 95959 
              (530) 401-8024 
              www.berkeleysolar.com 

------------------------------------------------------------------

              From: [email protected] 
[mailto:[email protected]] On Behalf Of Eric Thomas
              Sent: Saturday, March 26, 2011 2:09 PM
              To: [email protected]
              Subject: [RE-wrenches] Generator and Enphase

              I have a customer with a "30A Mechanically Interlocked Breaker" 
for their generator feed at the main panel. My question is: If the home power 
is transferred from utility to generator power, will the backfed PV see the 
generator as grid power and sync up and produce? This is a nice Honda Generator 
so the power should be fairly clean. Any experiences are appreciated.

              Take Care,


              Eric Thomas
              Solar Epiphany LLC
              (206) 919-3014
              www.solarepiphany.com


 _______________________________________________
              List sponsored by Home Power magazine

              List Address: [email protected]

              Options & settings:
              
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

              List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

              List rules & etiquette:
              www.re-wrenches.org/etiquette.htm

              Check out participant bios:
              www.members.re-wrenches.org




--------------------------------------------------------------------
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  <OneLine.JPG>_______________________________________________
          List sponsored by Home Power magazine

          List Address: [email protected]

          Options & settings:
          http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

          List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

          List rules & etiquette:
          www.re-wrenches.org/etiquette.htm

          Check out participant bios:
          www.members.re-wrenches.org




------------------------------------------------------------------------
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  _______________________________________________
      List sponsored by Home Power magazine

      List Address: [email protected]

      Options & settings:
      http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

      List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

      List rules & etiquette:
      www.re-wrenches.org/etiquette.htm

      Check out participant bios:
      www.members.re-wrenches.org




----------------------------------------------------------------------------
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  

------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Home Power magazine

  List Address: [email protected]

  Options & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to