the usual 208 3 phase is Y and not have high leg. sometimes you will measure up to 208 on the high leg of at Delta high leg to neutral. If it is Delta 3 phase 120-240 and a 200 about volt high leg, connect across the 240 volt legs, I e that is across each phase they should be 240 each leg to leg connect the neutral only if you have one in that phase. both Fronius and SMA have nice drawings in their installation guidelines or at their training courses.
________________________________ From: Aladdin Solar <[email protected]> To: [email protected] Sent: Thu, April 7, 2011 11:06:55 PM Subject: [RE-wrenches] PV to 208v 3-phase with high leg What is the best approach to interconnecting with a 208 volt 3-phase service having a high leg? Small to medium sized PV systems. Charlie Pickard Aladdin Solar
_______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org