To all,

After hooking a power quality meter up over night, it was the frequency causing 
the problem. Dips as low as 59 over night.  Problem was fixed ad all is well!

Thanks for the help and the links. 



Jesse

Sent from my iPhone

On Apr 7, 2011, at 8:05 PM, "Ryan J LeBlanc" <[email protected]> 
wrote:

> 
> In addition to David's insight, I would like to also offer this link for the
> manual:
> 
> http://www.sma-america.com/en_US/service/downloads.html
> 
> If you click on the "Archive" tab, documentation is available for all
> out-of-production units.
> 
> Also, http://www.SMA.de sometimes may have info that the US site doesn't.
> 
> ~ Ryan LeBlanc
> 
> ------------------------------
> 
> Message: 10
> Date: Thu, 07 Apr 2011 08:25:47 -0700
> From: David Katz <[email protected]>
> To: RE-wrenches <[email protected]>
> Subject: Re: [RE-wrenches] Sunny boy 1800
> Message-ID: <[email protected]>
> Content-Type: text/plain; charset="iso-8859-1"; Format="flowed"
> 
> Jesse,
> Here is one more thing to look at.  I have 3 SMA 1800 W inverters on my 
> house and had a very similar problem when I installed them.  They are 
> very sensitive to AC voltage.  Mine would turn off at 128 VAC.  My 
> utility voltage is 125 per leg and because of voltage "drop" in a log 
> run of wire, it would get over 128 when the inverters were putting out 
> power. This made it go on and off every 5 minutes.  I changed the 
> parameters through the Sunny WebBox and set the AC cut-off to 135 and 
> the problem went away.
> David
> 
> David Katz
> 
> Founder & CTO
> 
> AEE Solar
> 
> T(707) 825-1200
> 
> C(831) 325-9582
> 
> F(707) 825-1202
> 
> [email protected] <mailto:[email protected]>
> 
> www.aeesolar.com <http://www.aeesolar.com/>
> 
> 
> 
> On 4/6/2011 4:41 PM, Jesse Dahl wrote:
>> Wrenches,
>> 
>> I've been working on a sunny boy 1800 with some problems. There is no
> manual and SMA website does not have it available.  I need to watch the
> lights on the inverter to find the problem, but I'm not there now and I
> can't get this off my mind, so I will ask the esteemed members of this list.
>> 
>> When it's cloudy, the inverter comes on and loads the array. I can watch
> the sunny keeper watts reading rise until it get around 1000w and full sun
> hits the array.  Once full sun hits the array, the inverter drops out.  It
> did it three times to me today, and the inverter will not come on during
> full sun. Grid volts and hz are okay durning this.
>> 
>> I know it's impossible to troubleshoot like this, but anyone deal with
> problems like this?
>> 
>> 
>> Thanks for the help!
>> 
>> 
>> Jesse Dahl
>> 
>> Sent from my iPad!!!
>> _______________________________________________
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to