SMA does make such a device. It is called the Smart Load. 
"If there is an electricity surplus, the Smart Load feeds it into special 
loads, for example heating cartridges in a hot water tank. The control system 
is completely automatic, lightning fast and free of retroactive effects for 
other loads. This continuous and quick energy consumption allows for ideal 
protection of system components and guarantees increased reliability." (off our 
site).
This device is not UL listed, but can be obtained if desired.

It is possible to do this with other devices, just not sure of part numbers and 
such. I will look into it, if I find something I will let you know.

SMA America, LLC
Steve Jefferson
Sr. Technical Service Specialist, Sunny Family
6020 West Oaks Blvd, Suite 300
Rocklin, CA 95765 - 3714
U.S.A.
Tel:  +1 916 625 0870
Fax: +1 916 624-2445
Service Line +1 877 697 6283 (Toll Free)
Email: [email protected]
www.SMA-America.com
 
This email and any attachments thereto may contain SMA America, LLC 
confidential, privileged and private material for the sole use of the intended 
recipient. Any review, copying, or distribution of this email (or any 
attachments thereto) by others is strictly prohibited. If you are not the 
intended recipient, please contact the sender immediately and permanently 
delete the original and any copies of this email and any attachments thereto. 
Thank you.


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Mark Frye
Sent: Wednesday, April 13, 2011 10:36 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] AC Coupling Fronius IG Plus 10.0 inverter

Thanks Brian,

My understanding is that the SI/SB combination is the only grouping of
equipment that provides proportional control of the output of the AC coupled
inverter.  

But, this is what is love about AC coupling, there are so many ways to skin
so many different kinds of cats. I really like the DC diversion side
solution if you have someplace to put the power instead of just the
batteries, although that might be generally less commonly available for
retrofits into existing on-grid households.

Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City,  CA 95959
(530) 401-8024
www.berkeleysolar.com 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brian Faley
Sent: Wednesday, April 13, 2011 10:21 AM
To: [email protected]
Subject: Re: [RE-wrenches] AC Coupling Fronius IG Plus 10.0 inverter

Esteemed Wrenches,

There are other battery based inverters with Frequency Shift for use in AC
coupled systems. Magnum MS4024PAE and MS4448PAE models shift the output
frequency + >0.5Hz based upon battery voltage. On 24V models the set point
is 0.2V above absorb voltage, and on 48V models it is 0.4V above absorb. It
will protect the battery against overcharge by dropping the AC coupled Grid
tied inverter offline. It can be used as a method of regulating AC coupled
grid tied systems, but works best when there is a DC side diversion load
controller.

Brian Faley
Chief Engineer
Magnum Energy
2111 W Casino Rd
Everett, WA 98204
425-353-8833
[email protected]
 
> ------------------------------
> 
> Message: 3
> Date: Tue, 12 Apr 2011 21:37:06 -0700
> From: "Mark Frye" <[email protected]>
> To: <[email protected]>,   "'RE-wrenches'"
>       <[email protected]>
> Subject: Re: [RE-wrenches] AC Coupling Fronius IG Plus 10.0 inverter
> Message-ID: <0FAC7002A96948B598E5EF79FF3D77E6@marksdell>
> Content-Type: text/plain; charset="us-ascii"
> 
> Gary,
> 
> I have been looking at some AC coupled stuff lately. The "FSC" is 
> propriatary to SMA, Sunny Island to Sunny Boy.  Pretty much anything
else
> you need something to sense the voltage of the battery bank so you can 
> open a contactor on the AC line to the Fronius when the battery 
> voltage
gets
> too
> high. Once the voltage drops the contactor can close and bring the
Fronius
> back on line and then the 5-minute start up delay before it is feeding
the
> line again.
> 
> Mark Frye
> Berkeley Solar Electric Systems
> 303 Redbud Way
> Nevada City,  CA 95959
> (530) 401-8024
>  <http://www.berkeleysolar.com/> www.berkeleysolar.com

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to