Also, it sounds like you're losing almost 7 volts at times, which would 
correspond to 3 to 4 batteries in failure. 
I think that would be very unlikely, hence why I still vote for the connectors 
being at fault. Possibly, it may just be one of the main connectors, and as 
others pointed out already:
it probably will only show itself under load. Don't forget to check the 
connections at the main disco and inverter too.
I had a system act very similar that was just a single connection that the 
customer had loosened and forgot to retighten.

R. Walters
[email protected]
Solar Engineer




On Apr 20, 2011, at 5:01 PM, Allan Sindelar wrote:

> It wouldn't cost much to replace the 5 interconnects, if only to eliminate 
> the issues that Ray has mentioned from consideration.
> 
> Also, Rich, you didn't mention if all of the terminals got hot, or only 
> one/few/some. If the terminal contacts or the interconnects are at fault, I 
> would expect that some would be noticeably hotter than others, corresponding 
> to specific high-resistance issues at those terminals.
> Allan
> 
> Allan Sindelar
> [email protected]
> NABCEP Certified Photovoltaic Installer
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> Positive Energy, Inc.
> 3201 Calle Marie
> Santa Fe, New Mexico 87507
> 505 424-1112
> www.positiveenergysolar.com
> 
> 
> 
> 
> On 4/20/2011 2:38 PM, R Ray Walters wrote:
>> 
>> Sounds like problem connections, if all the cells are an even 2.12 v. 
>> I wouldn't solder 4/0 connections, the solder can run back up the cable 
>> stranding, and make the cables too stiff to fully connect with the battery 
>> terminal. 
>> I had a battery terminal meltdown due to this. We quit using thick bussbars, 
>> soldered cables, and stiff (THHN) cables at battery terminals.
>> Also if not soldered properly, you can actually create more resistance in 
>> the connection due to oxidation and pockets of flux.
>> Cables from the manufacturers (HUP, Outback, Trace) are not soldered BTW. 
>> Its possible that heating the terminals when soldered (with a torch?) may 
>> have created a layer of oxidation that is causing the resistance (internally 
>> or externally)
>> Sand the contact surfaces, and see if that helps.
>> 
>> Get an infrared thermometer (fairly cheap these days at Sears or automotive 
>> store) and check all the connections under load.
>> Also, check the voltage drops on your cables under load, you should be able 
>> to find where all that voltage is going, and it should match your infrared 
>> readings.
>> I'd also take out another set of cables to see what that does.
>> 
>> R. Walters
>> [email protected]
>> Solar Engineer
>> 
>> 
>> 
>> 
>> On Apr 20, 2011, at 1:15 PM, Bob-O Schultze wrote:
>> 
>>> Rich,
>>> It sounds like you've got a rotter or two. Given the short age of the pack, 
>>> that's my suspicion. Try checking the individual battery voltages when 
>>> under load and fairly well discharged. I've seen a new battery bank all 
>>> show good SG and individual voltages while resting but one or more 
>>> batteries tank badly under load. Poor manufacturing QC is the cause.
>>> good luck, Bob-O
>>> 
>>> On Apr 20, 2011, at 12:03 PM, Rich Nicol wrote:
>>> 
>>> RE Wrenches
>>> My question regards a system (installed by homeowner / friend) where they 
>>> recently upgraded their t105 battery bank to Trojan RE series L16 2 volt 
>>> cells.  The battery bank consists of 6 batteries in series for a 12 volt 
>>> system.  The interconnects are 12” long 4/0 cables with crimped and 
>>> soldered lugs.  Main cables are 6’ long 4/0 cables.
>>> The first issue is high terminal temperature during periods of heavy draw 
>>> (~100 amps @ 12v when water pump is on).  Due to the issue the owner has 
>>> been only running the water pump when charging the batteries with his 
>>> generator since the transfer switch on the Outback inverter has transferred 
>>> his household circuits from the battery bank to the generator.  Obviously 
>>> this is an inconvenience. Before the end of life on his T105’s he had no 
>>> issues with the 6 volt cells in series/parallel using only #2 AWG 
>>> interconnects.
>>> Most recently he’s experienced an issue where the inverter will not come on 
>>> at all and when attempted to come by switching on his main DC breaker  the 
>>> voltage at the batteries sags from 12.5 to ~5V!  This issue is not with the 
>>> inverter since I loaned him a back up Trace DR I keep around as a loaner 
>>> but it too would not come on and voltage sagged as well.  This sag is with 
>>> no demand since it sags immediately when the DC breaker is switched on when 
>>> connected to the inverter even though the inverter has not been switched 
>>> on. 
>>> I stopped by this AM to check out the situation, specific gravity of all 
>>> cells is good, open circuit voltage on each cell is matched at 2.12  volts. 
>>>  The battery bank is                             only about 4 months old.
>>> Any insight would be greatly appreciated.
>>>  
>>> Battery specs:
>>> 2 volt, Rated Capacity @ 5 Hr rate=909 AH, 20 hr rate = 1110 AH, 100 hr 
>>> rate = 1235.
>>>  
>>> Thanks for your help!
>>> Rich
>>> 
>>> 
>>> 
>>> _______________________________________________
>>> List sponsored by Home Power magazine
>>> 
>>> List Address: [email protected]
>>> 
>>> Options & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive: 
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out participant bios:
>>> www.members.re-wrenches.org
>>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Home Power magazine
>> 
>> List Address: [email protected]
>> 
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out participant bios:
>> www.members.re-wrenches.org
>> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to