Re: [RE-wrenches] Air conditioning for batteries in highPartially right, Jim. 
Except hotter internal temperatures cause the electro-chemical process to be 
faster, not slower. Only as temperatures decrease below 25C, which may vary 
with manufacturer, is the process slowed.

Larry
  ----- Original Message ----- 
  From: North Texas Renewable Energy Inc 
  To: RE-wrenches 
  Sent: Friday, April 22, 2011 12:54 PM
  Subject: Re: [RE-wrenches] Air conditioning for batteries in hightemperature 
climate


  It's the efficiency of the chemical reaction that creates the loss. The 
electrolyte solution cannot pull out nor put back the same amount of 'energy' 
in hotter or colder conditions. When temperatures moderate, the chemical 
reaction returns to its nominal efficiency. The batterys capacity should not be 
permanently affected unless SOC reaches extreme levels. 
  Or that's how I recall the process explained for cold temps. I assume the 
same is true for high temps.
  Jim

    -----Original Message-----
    From: [email protected] 
[mailto:[email protected]]On Behalf Of Hugh
    Sent: Friday, April 22, 2011 2:13 PM
    To: RE-wrenches
    Subject: Re: [RE-wrenches] Air conditioning for batteries in high 
temperature climate


    Hi Roy,


    Hi temperatures will hit the battery capacity but will the battery 
efficiency be that much affected?  If the battery capacity is inadequate then 
you need to compare the aircon running cost to the cost of buying a 10% larger 
battery.  Don't you?


    Cheers


    Hugh




      Bob is correct, I do have an off grid client that uses an AC unit to keep 
the batteries cool.
      Although we're not in a high temp climate, it does get into the 80's and 
low 90's here
      in the summer.

      By my calculations, he was losing an 'average' of 10% storage capacity 
during the 5 month
      period from late spring to early fall. In July and August it was closer 
to 18%, but for calculation
      purposes, 10% is close enough. His bank capacity is 4800AH @ 48 VDC. 
That's 230,400 watt hours
      and 10% of that rounds out to 23,000 watt hours lost to heat.

      I showed up one day to check something in the power shed and was dismayed 
to see a window
      AC unit installed there. An interesting customer discussion ensued and I 
had to admit he was
      correct in his calculations.

      The Energy Star rated AC unit consumes no more than 3,000 watt hours per 
day, even in the
      highest heat. Essentially, he's 'spending" 3 kilowatt hours to 'buy back' 
20 kilowatt hours of
      storage. He got me on that one!

      That reasoning didn't work on the 6 other AC units that appeared on his 
house the following
      week. But that's another story altogether!
      Roy Butler
      NABCEP Certified Solar PV Installer®
      NYSERDA eligible PV & wind installer
      PA Sunshine Program Approved PV Installer
      Four Winds Renewable Energy, LLC
      8902 Route 46
      Arkport, NY 14807
      607-324-9747

      www.four-winds-energy.com

      Although no trees were killed in the sending of this message,
      a large number of electrons were terribly inconvenienced.

                     

      On 4/22/2011 7:40 AM, bob ellison wrote:

        I believe Roy has a customer with a huge battery bank that air 
conditioned the battery room. He ran the numbers and the air conditioning 
actually made sense.


         
        Bob Ellison


         
        From: [email protected] 
[mailto:[email protected]] On Behalf Of R Ray Walters
        Sent: Thursday, April 21, 2011 4:50 PM
        To: RE-wrenches
        Subject: Re: [RE-wrenches] Air conditioning for batteies in high 
temperature climate


         
        Are you using temperature compensation? It lowers the voltage when its 
hot.

        Also, have you considered setting the batteries in a below ground 
vault? I've had good luck with in floor battery boxes.

        Finally, AGMs and L16s just don't last very long anyway. AGMs maybe 3 
years, and L16s I've seen die in under 5 years and we get to 15 below zero.

        My suggestion: temp comp, ground vault, HUP or equivalent cycle life.


         
        R. Walters

        [email protected]

        Solar Engineer


         

         




         
        On Apr 21, 2011, at 1:22 PM, Starlight Solar, Larry Crutcher wrote:




        Hello Battery Wrenches,


         
        Over the years I have had several battery banks in Baja and Sonora 
Mexico fail in just 36 to 48 months. These have been L16 or 8D AGM or flooded 
banks, 24 and 48 volt systems. The charging systems are working properly and 
programmed to manufacturer recommended set points and discharges are rarely 
over 30% DoD.  Some batteries are only used on weekends, some are discharged 
daily.  I believe what is affecting the short life is the high temperature they 
live in for 5 months each year. Temps. can hit 115 F in vented battery rooms. I 
have been thinking about a small air conditioner and insulated battery box to 
keep the battery at no more than 80 F. There are some portable units that draw 
about 600 watts and the run time would be very little with a highly insulated 
enclosure. There is ample power to do this on the home I am changing batteries 
in now. Has anyone done this and gained longer battery life?


         
        Best Regards,


        Larry Crutcher
        Starlight Solar Power Systems

        powered by STARLIGHT

        _______________________________________________
        List sponsored by Home Power magazine

        List Address: [email protected]

        Options & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm

        Check out participant bios:
        www.members.re-wrenches.org


         


        _______________________________________________
        List sponsored by Home Power magazine

        List Address: [email protected]

        Options & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm

        Check out participant bios:
        www.members.re-wrenches.org


      _______________________________________________
      List sponsored by Home Power magazine

      List Address: [email protected]

      Options & settings:
      http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

      List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

      List rules & etiquette:
      www.re-wrenches.org/etiquette.htm

      Check out participant bios:
      www.members.re-wrenches.org




-- 
Hugh Piggott

    Scoraig
    http://www.scoraigwind.co.uk


------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Home Power magazine

  List Address: [email protected]

  Options & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to