Hi Hugh, An AGM battery is considered full when the current drops below a specified amount. Lifeline, for instance, is considered full when current is less than 0.5 amps per 100AH. The Blue Sky Energy IPN Pro Remote http://www.blueskyenergyinc.com/products/details/ipn_proremote/ will allow you to program the transition into float mode based on the amount of current flowing through a shunt. This can be very useful for your project that involves opportunity charging. Multiple charge sources can be monitored by the IPN Pro simultaneously. For us, it is the most ideal charger for VRLA batteries.
Here's a link to some charging instructions for the Fullriver AGM: http://www.fullriver.com/products/admin/upfile/Charginginstruction.pdf Larry ----- Original Message ----- From: "Hugh" <[email protected]> To: "RE-wrenches" <[email protected]> Sent: Sunday, April 24, 2011 12:11 AM Subject: Re: [RE-wrenches] AGM battery charging, more details | Thanks, Larry for the detailed response | > | > | >Generally, the manufacturers charge recommendations should be followed. | | Yes but the issue I have is to know when and how to switch from | absorption to float. The Tristar has its own decision process but is | it correct? And if not then are the settings suitable. | | > If you take away the red paint, I believe the Rolls AGM is the | >Fullriver DC series battery. We started selling Fullriver last year | >and I was surprised to find the very high absorb voltage | >recommendation. For the DC400-6 (415AH) in cycle use they recommend | >charging at 29 to 29.8 volts and float at 27.6 @25C! That is the | >highest AGM voltage settings I have seen from any manufacturer. | | That's my worry. | | > | >My thinking about AGM's is that the float voltage and transition | >current are much more important factors than absorb voltage and | >current. | | Transition current is not in the vocabulary of the Tristar | controller. I am not aware of a product that has this feature aside | from maybe some inverters. I have read in an Outback manual that | you should program the absorb time based on charge current | measurements, but the logic of this depends on the battery being | 'flat' to the same degree at the start of each charge - whereas wind | and solar charging is not like that. | | >For most AGM's, initial charge current is almost unlimited. However, | >Fullriver recommends current limiting and constant voltage for the | >bulk/absorb cycle. Their current limit is .15 to .35*C20 rate. BTW, | >make sure to adjust the temp. comp to 3mV/C/C for float. That is | >lower than most. | | Tristar default is 5 mV/C/C but can be modified by RS232 lead and | software intervention. | | > | >Equipment in a 24 volt system should be fine up to 32 to 33 volts. | >Check the specs. | | It's not me that has the problem it's the telemetry engineers. I | assume they read the manual. But reduced temp comp helps. | | > | >What I said about equalizing was that I had done it twice to my | >personal AGM battery bank. After the battery is fully charged (<0.2A | >per 100ah @ C20) I put each battery, not each string, on a current | >controlled charger. The current setting is .05*C20. | | That is 5 amps for a 100Ah battery? Does this not make them gas? | | >I don't use voltage regulation when I do this. Once the battery | >reaches 2.58 V/Cell, I charge for about 4 more hours always | >monitoring battery temperature. I use this process to recover AGM | >battery capacity and it has been mostly successful with all | >brands. No more puzzle. | | Thanks - AGMs are a puzzle to me but you make it sound pretty simple. | I do still have an issue with controlling the charge rate using | existing technology on an opportunity charging system where the | battery may be in any state of charge when the wind starts blowing, | or sun starts to shine. | | best wishes, | -- | Hugh Piggott _______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org

