Hi Peter,

The AIR units are designed for battery charging, so unless you are installing 
an AC coupled system using Enphase inverters along with a battery-based 
inverter this won't be easy and maybe not possible. If you are planning a 
battery-based inverter in the system, and you use the AIR to charge the battery 
bank on the DC side, the battery-based inverter will need to be a grid-tie 
model, like a Schneider XW or an OutBack GFX (the battery-based inverter does 
not need to be a grid-tie model in a more typical AC coupled system).

Give SWWP a call to see if they have ever tried to grid-tie an AIR 403, AIR-X, 
or AIR Breeze using an Enphase inverter. I don't think that the AIR's 
controller will operate without a battery, but I'm not sure. Maybe an AIR 
Industrial would work as it doesn't have a built-in controller. You would need 
to use a 24V model to get into the DC voltage range of the Enphase.


Brian Teitelbaum
AEE Solar



From: [email protected] 
[mailto:[email protected]] On Behalf Of Peter Talmage
Sent: Thursday, May 05, 2011 10:26 AM
To: RE-wrenches
Subject: [RE-wrenches] Interfacing an Air 403 wind generator

I have a client with an independent power system who is going utility 
interfaced. We are putting the 24 volt arrays on Ephase inverters. He wants the 
Air 403 to be interfaced as well. Has anyone done this and if so, how ?  Thanks

Peter Talmage, P.E.

Energy and Design


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to