Fella's,I'm using the Viper Model 5026 refractometer ... 5026 ... My brother 
who is a heavy duty mechanic ordered it for me a few years ago from his Mac 
Tool dealer after i was 'venting' about getting inaccurate readings from a 
hydrometer.  Cost was about $80.  Came with a hard plastic case that also held 
a vial of distilled water (for calibration), eye-dropper, special cleaning 
cloth and calibration screwdriver.Calibration should be done before each use 
(whole bank not per cell) so that the temperature compensation will be accurate 
to your surroundings.  If the ambient temp is fluctuating while testing then 
you should re-calibrate often.  That is to say, when you calibrate it, it is 
corrected to the present ambient temperature.
Jay, cleaning btwn cells..... what i do is keep two rags/shop towels handy.  
One, i keep on top of the batteries for setting the battery cap (that i'm 
testing) and the eyedropper on when i'm not using it (to keep the battery tops 
clean and dry)  With the other towel, after testing each cell i wipe the optic 
lens surface clean and dry just like the Care/Maintenance instructions say 
"...must be thoroughly wiped clean and dry after each use" (-to ensure accurate 
readings)
I have noticed if there is any residue or smudge on the optic lens (not 
thoroughly cleaned) then the indication line is distorted and not 'sharp' and 
will vary the reading by +-0.005.
benn
DayStar Renewable Energy Inc. [email protected] HAVE A SUNNY DAY







> From: [email protected]
> Date: Mon, 16 May 2011 11:47:29 -0700
> To: [email protected]
> Subject: Re: [RE-wrenches] Fwd:  Hydrometer source
> 
> Hi Jeff,
> 
> How much do you "clean or rinse" your unit between each cell?
> 
> I'm trying to figure out how much  I need to do between each test.
> 
> thanks,
> 
> 
> jay
> 
> peltz power

                                          
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to