Dan, I think we're only looking at an error of 20 minutes per (8760 hrs x 60 min / hr) = 0.00381%, well within the frequency drift allowed under UL 1741. So as you point out, it would only be the shorter excursions away from 60.0Hz that would be the issue. This shift isn't the easiest thing in the world to do (and then maintain)!

On 2011/6/27 15:08, Exeltech wrote:
A max of 20 minutes error per year (as stated in the article)
equates to an error of 0.228%.

Whether grid-tied inverters stay on line or not depends on
the ultimate range of the frequency excursions permitted
during the tests. UL1741 limits are 59.3 to 60.5 Hz for
fixed frequency settings. The cumulative error shown
above is well within those bounds. 59.3 Hz = -1.16%;
60.5 Hz is +0.83%.

However, I could see cases where they may allow 60.6 Hz
one day and 59.4 Hz the next. The overall net difference
would be zero for a frequency-dependent clock - but a
grid-tied inverter would spend the first day of this example
totally offline.

This would have to be a grid-wide frequency difference,
else they'd end up with some seriously large power flows
from one part of the grid to another, with potentially disastrous
results.

It will be interesting to see how they handle this.

Thanks for the post.

Dan


--- On *Sun, 6/26/11, bob ellison /<[email protected]>/* wrote:


    From: bob ellison <[email protected]>
    Subject: Re: [RE-wrenches] National grid hertz adjustment
    To: "'RE-wrenches'" <[email protected]>
    Date: Sunday, June 26, 2011, 6:40 PM

    This will make it interesting to everybody with a grid tie inverter,
    can we open up the specs to let them work with the “new test
    variation”? The other option is that the inverters will spend a lot
    more time off line.

    Bob Ellison

    *From:*[email protected]
    [mailto:[email protected]] *On Behalf Of
    *Roy Butler
    *Sent:* Sunday, June 26, 2011 1:45 PM
    *To:* RE-wrenches
    *Subject:* Re: [RE-wrenches] National grid hertz adjustment

    I saw this as well, came over the AP news wire on Friday, June 24th.
    I've been trying to figure out what they hope to gain by allowing more
    frequency variation.....puzzling at best!

    Roy Butler

    NABCEP Certified Solar PV Installer®

    NYSERDA eligible PV&  wind installer

    Four Winds Renewable Energy, LLC

    8902 Route 46

    Arkport, NY 14807

    607-324-9747



    www.four-winds-energy.com  <http://www.four-winds-energy.com>



    Although no trees were killed in the sending of this message,

    a large number of electrons were terribly inconvenienced.






    On 6/26/2011 1:31 PM, North Texas Renewable Energy Inc wrote:

    This article in the local paper sounds a little like potential
    trouble for grid connected inverters. I looked around on the NERC
    www site without finding the report mentioned. Any other wrenches
    seen anything about this experiment?

    Jim Duncan

    By Seth Borenstein The Associated Press

        WASHINGTON -- A yearlong experiment with the nation's electric
        grid could mess up traffic lights, security systems and some
        computers -- and make plug-in clocks and appliances like
        programmable coffee makers run up to 20 minutes fast.

        "A lot of people are going to have things break, and they're not
        going to know why," said Demetrios Matsakis, head of the time
        service department at the U.S. Naval Observatory, one of two
        official timekeeping agencies in the federal government.

        Since 1930, electric clocks have kept time based on the rate of
        the electrical current that powers them. If the current slips
        off its usual rate, clocks run a little fast or slow.

        Power companies now take steps to correct it, keeping the
        frequency of the current as precise as possible.

        The North American Electric Reliability Corp., which oversees
        the U.S. power grid, is proposing an experiment that would allow
        more frequency variation without corrections, according to a
        June 14 company presentation obtained by The Associated Press.

        The test is tentatively set to start in mid-July.

        Tweaking the power grid's frequency is expensive and takes a lot
        of effort, said Joe McClelland, head of electric reliability for
        the Federal Energy Regulatory Commission.

        "Is anyone using the grid to keep track of time?" McClelland
        said. "Let's see if anyone complains if we eliminate it."

        No one is quite sure what will be affected. This won't change
        the clocks in cellphones, GPS or even on computers.

        But wall clocks and those on ovens and coffee makers -- anything
        that flashes "12:00" when it loses power -- may be a bit off
        every second, and that error can grow with time.

        VCRs or DVRs that get their time from cable systems or the
        Internet probably won't be affected, but those with clocks tied
        to the electric current will be off a bit, Matsakis said.

        According to the June presentation, East Coast clocks may run up
        to 20 minutes fast over a year, but West Coast clocks are only
        likely to be off by eight minutes. In Texas, it's only an
        expected speedup of two minutes.


        Read more:
        
http://www.star-telegram.com/2011/06/24/3178359/test-of-electric-grid-could-be.html#ixzz1QOzHwezw


        
<http://www.star-telegram.com/2011/06/24/3178359/test-of-electric-grid-could-be.html#ixzz1QOzHwezw>



_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options&  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules&  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to